Wouldn't that be paralleling them?You are going to splice the grounds together and pigtail a ground to bond the box, right?
And thats not an issue...Wouldn't that be paralleling them?
Where in the NEC does it require all the grounds be spliced together?stickboy1375 said:And thats not an issue...
No not on the ground due it is not a current carry conductor at all.Wouldn't that be paralleling them?
All the grounds need to be spiced together and the box bonded.
That I been doing on both side of USA and France for many years and never have a issue with that at all.And thats not an issue...
I havent check the NEC for a little while but I can able dig it up when I get to my office and find out with it. Our French codes do requried that it have to be spliced together by either wirenut or wago or block connector or screw on the metal box one of metholds are approved for this purpose.Where in the NEC does it require all the grounds be spliced together?
Let me dig it up, but it does exist.Where in the NEC does it require all the grounds be spliced together?
If you don't have a ground whose path isn't continuous back to the primary ground, you will have an ungrounded load. I don't need the NEC to tell me that is dangerous.Where in the NEC does it require all the grounds be spliced together?
His question was about bonding the grounds of two separate circuits, in a common box.JulieMor said:If you don't have a ground whose path isn't continuous back to the primary ground, you will have an ungrounded load. I don't need the NEC to tell me that is dangerous.
It's just redundancy, to ensure proper ground fault protection.So, to me, the obvious next question is, "why?" Let's assume there is a junction box with conductors from two separate circuits. Lets assume one circuit is 20 amp and one is 15 amp. Lets also assume that only the EGC from the 20 amp circuit is bonded to the box, and that the two EGCs of both circuits are NOT bonded at this box. What is the danger which serves as a basis for the code requirement?
250.148 Continuity and Attachment of Equipment Grounding Conductors to Boxes.
Where circuit conductors are spliced within a box, or terminated on equipment within or supported by a box, any equipment grounding conductor(s) associated with those circuit conductors shall be connected within the box or to the box with devices suitable for the use in accordance with 250.148(A) through (E).
Exception: The equipment grounding conductor permitted in 250.146(D) shall not be required to be connected to the other equipment grounding conductors or to the box.
(A) Connections. Connections and splices shall be made in accordance with 110.14(B) except that insulation shall not be required.
(B) Grounding Continuity. The arrangement of grounding connections shall be such that the disconnection or the removal of a receptacle, luminaire, or other device fed from the box does not interfere with or interrupt the grounding continuity.
(C) Metal Boxes. A connection shall be made between the one or more equipment grounding conductors and a metal box by means of a grounding screw that shall be used for no other purpose, equipment listed for grounding, or a listed grounding device.
(D) Nonmetallic Boxes. One or more equipment grounding conductors brought into a nonmetallic outlet box shall be arranged such that a connection can be made to any fitting or device in that box requiring grounding.
(E) Solder. Connections depending solely on solder shall not be used.