Registered
Joined
·
5 Posts
Discussion Starter #1
i have 200amphouse panel 100amp in garage #2al 2 hots 1n no ground neutral was bonded to box in garage whats wrong with this:vs_OMG:
 

·
Licensed electrician
Joined
·
13,387 Posts
Perhaps nothing. Is the garage detached? What size breaker feeds the garage?
 
  • Like
Reactions: res1kk8t

·
A "Handy Husband"
Joined
·
11,814 Posts
Depending on when it was done and what other services extend to the garage, maybe nothing.

Prior code allowed such a circuit if no other metallic service (metal water pipe,cable TV, telephone) are extended to the garage. Also ground rod(s) required at the garage. Under those conditions the neutral and ground are bonded at that sub panel.
 

·
Registered
Joined
·
5 Posts
Discussion Starter #4
ihave 100amp breaker in house 200amp box line going to attached garage 100amp box in garage was told 100amp box neutral was not to be bonded
 

·
A "Handy Husband"
Joined
·
11,814 Posts
Aha, attached garage, different story. Needs to be a 4 wire circuit, no ground rods, no bond between neutral and ground.

Is there a breaker in the main panel feeding the sub? What size?
 

·
Registered
Joined
·
5 Posts
Discussion Starter #6
100amp in main200amp panel to garage 100amp box what wire size from 100amp breaker in main to 100amp box in garage
 

·
Licensed electrician
Joined
·
13,387 Posts
What is the wiring method between panels?
 
  • Like
Reactions: res1kk8t

·
Licensed electrician
Joined
·
13,387 Posts
Cable? Metal conduit?
 

·
Licensed Electrical Cont.
Joined
·
7,829 Posts
ihave 100amp breaker in house 200amp box line going to attached garage 100amp box in garage was told 100amp box neutral was not to be bonded
Again.......it all depends on when the job was done. For a sub-panel in a detached structure for many years it was code acceptable to run a "3-wire" feeder and bond the neutral. Just like it was code to run a "3-wire" circuit to an electric dryer or range.
 
  • Like
Reactions: res1kk8t

·
Licensed electrician
Joined
·
13,387 Posts
SER should have an insulated neutral and a bare ground as well as the two hots.
 
  • Like
Reactions: res1kk8t