Current setup:
125 amp main breaker disconnect outside next to the meter box
It feeds a panel that does not have a main breaker.


Replacement system:
200 amp exterior panel with feed through
Same 125 amp panel inside


The feed through wires will feed the panel inside. Does there need to be a separate 125 amp breaker to the panel. The same gauge wire will be going from the feed through lugs to the main panel.
 

· Registered
Joined
·
85 Posts
Except for panelboards where more than 90% of the overcurrent devices supply feeders or motor branch circuits, every panelboard shall be protected on the supply side by overcurrent devices having a rating not greater than that of the panelboard.
 

· Registered
Joined
·
328 Posts
Discussion Starter · #7 ·
To clear up some confusion, the wire that goes to the existing panel box inside will be using the existing wire. The wire will not be upgraded. The only wire that will increase in size will be the wire from the new exterior 200 amp panel to the meter, and the wire from the meter to the utility service.


Let's say there was never a main breaker panel outside and the meter direct fed the panel inside that does not have a main breaker. Would that be up to code? Does there always need to be a main breaker somewhere in the circuit?
 

· Registered
Joined
·
328 Posts
Discussion Starter · #10 ·
Thanks

Just to clarify, one couldn't just use the proper load calculation of the existing breakers for overcurrent protection.

What would be an adequate solution in my situation? I've had 3 electrician quotes. They all recommended replacing the 125 amp exterior panel (that has a single 125 amp breaker) with a 200 amp 4/8 panel. The new heating and air conditioning would be run off the exterior.
 

· Registered
Joined
·
328 Posts
Discussion Starter · #12 ·
Their quote didn't include reconnecting the subpanel?
The solution is to use two of the four spaces for a 125 amp 2 pole breaker.

It doesn't state specifics. You're saying that the 125 amp breaker would need to be setup as a back feed. They were stating that feed through panels would be used (connections to the house panel made at the bottom of the bus bar.
 

· Registered
Joined
·
85 Posts
Your new panel should be a 200A Nema 3R minimum rated for service enterance outside. Get a larger panel, an 8 circuit or larger.

Install a 125A double pole breaker and terminate the old feeder to your panel to it. No feed through panel.

Be sure to remove your grounding conductor from your sub panel. It will be bonded to your main, but not taken to ground.
 

· Master Electrician
Joined
·
4,735 Posts
Your new panel should be a 200A Nema 3R minimum rated for service enterance outside.

Install a 125A double pole breaker and terminate the old feeder to your panel to it. No feed through panel.

Be sure to remove your grounding conductor from your sub panel. It will be bonded to your main, but not taken to ground.
You stil need a grounding conductor to the panel. The neutral/ground bond must be removed.
 

· Registered
Joined
·
775 Posts
Right. You're putting in what sounds like a ranch style meter main with distribution. You'll have 8 circuits you can distribute out of the meter main. Two of those circuits will be for your existing sub panel on a 125A 2 pole breaker. 125A breakers take up two whole spaces so you'll have four circuits left to distribute out of your meter main. It sounds like the A/C will take up at least two of those so you'll be left with two circuits spare in the meter. The feed through lugs are nice because you can put another 200A sub panel with tons of space off them if ever needed.
 

· Registered
Joined
·
328 Posts
Discussion Starter · #19 ·
That's kind of what I originally planned. I figured 6 of the 8 slots would be used up. It would contain a 125 and two 30 amp double pole breakers.

I called one of the electricians and he confirmed that it would be wired through the feeder terminals (no 125 amp breaker).
 

· Registered
Joined
·
775 Posts
Then I'm missing a piece of info or the electrician is not following code. You have 4 spaces and 8 circuits for distribution. Any breaker over 50A will take a full space thus reducing the available circuits remaining for distribution by 2.
 