I am installing a generic air flow duct to allow some outside air into my workshop during the warmer months. The duct is in a really high spot and I didnt want to use a manual damper so I purchased an electric inline damper to allow me to close it from a switch in the winter months.

Now I am trying to wire it to a switch instead of a thermostat (the directions say a Low Voltage thermostat is required). The instructions can be seen here:

http://suncourt.com/ZoneMaster_Instructions.html

Basically I want to know if I can use a standard single pole switch in place of the low voltage thermostat mentioned in the installation instructions.

And if NOT, what other options do I have to switch this instead of using a thermostat?

Any thoughts are appreciated!!!
 

· Registered
Joined
·
780 Posts
You can connect the transformer to 120 VAC and install the switch in the low voltage line in place of the thermostat connection or wire the transformer direct the the dampener and use the switch to turn the 120 VAC on and off the the transformer.
 

· Registered
Joined
·
2,294 Posts
You can connect the transformer to 120 VAC and install the switch in the low voltage line in place of the thermostat connection or wire the transformer direct the the dampener and use the switch to turn the 120 VAC on and off the the transformer.
I like your idea of switching the transformer. Then when its turned off, absolutely no power will be used.
 

· You talking to me?
Joined
·
7,551 Posts
the power used by a small transformer is minimal and switching the 120 voltage means he will have to install cabling and or conduit and boxes etc as required per code.

the low voltage wiring can be a phone line run across the floor if he wants.
 

· Registered
Joined
·
2,294 Posts
the power used by a small transformer is minimal and switching the 120 voltage means he will have to install cabling and or conduit and boxes etc as required per code.

the low voltage wiring can be a phone line run across the floor if he wants.
What you say is true, unless he uses a lamp cord switch and plugs it into a receptacle.
I wonder what the current rating for this damper would be.
As the damper will only be operated for awhile in the summer, why not have all shut off for the rest of the year!
 

· Registered
Joined
·
158 Posts
Discussion Starter · #9 ·
exterior t-stat? I thought you said this was in a workshop.
Yeah but I dont want it to open when I have my heat on in the shop in the winter, so an interior t-stat is really useless. If it was outside then it would work, but I am not keen on putting t-stat outside :)

I will just switch it. i purchased a N/C (Normally Closed) damper so I will actually only have to give it juice to open it during the summer and here in Montana that is only 4-5 months if we are lucky :)

Thanks, I can always count on this forum for solid advice (8 out of 10 times anyways :)

L8R
 

· yeah, right
Joined
·
142 Posts
Most damper actuators don't use much power, typically a couple of watts at 24vac. An old sprinker timer transformer plugged into a switched receptacle would be another option.
 