my 15amp circuit breaker is loose,vibration is causing to lose power on the circuit,the breaker doesn't trip.should i tighten or just replace the breaker?
 

·
Electrical Contractor
Joined
·
3,368 Posts
Is the breaker loose on the bus bar of the panel? Or is the bus bar corroded or pitted?

If you have an old worn out breaker, replacing it may be the answer.

If your panel has corroded or pitted bus bars, then a new breaker is only flushing good money after bad. You'll have to replace the panel in that case.
 

·
Registered
Joined
·
1,543 Posts
What brand do you have?

When you take the breaker out (WHEN ITS OFF!) Is the bus burnt, corroded, pitted, etc?

Is the breaker warped as if it was hot?
 

·
Registered
Joined
·
4,470 Posts
Tighten? Are you saying the breaker is bolted in? If it is tighten it. Power off main breaker first.
 

·
Registered
Joined
·
2,294 Posts
Some breakers have a screw that connects it to the pole bus! Other have a press connector.
Possibly, the screw wasn't tightened properly when it was installed. or it wasn't pressed into place properly.
As it was loose, damage may have occured where the breaker contacts the bus.
If you cannot tighten the mounting screw, you may be able to relocate the breaker to a spare position.
If you have no spare positions, try a new breaker.

REMEMBER TO TURN OFF THE MAINS BEFORE WORKING IN THE PANEL!
 