After reading a bunch of posts on sub-panels to garages and outbuildings, I have formed a plan of attack. In that I am not an electrician by any stretch of the term, I would appreciate a little validation or correction before I buy materials and pull wires ( I will have a licensed electrician do the actual connection, I think). So:
Distance from my outbuilding subpanel to main 200 amp panel in house is a total of 150'
Wires to go through 2" diam underground PVC conduit with large diam. bends each end (It already exists and feeding a fish tape was a piece of cake!)
Outbuilding to be a "typical" small workshop, with table saws, band saw, drum sander, of which only one tool would be on at one time. Maybe 8 additional GFCI outlets and assorted lighting to be powered her as well.
Will install 100 amp sub-panel in outbuilding, controlled by 60 amp breaker at main panel power feed.
I believe that pulling 3 #4 copper wires and one #8 copper ground, all in exterior weatherproof casing will be the right mix of wires (THIS is what I am most uncertain about!! - Comments??)
I believe that the neutral and ground bar need to be disconnected at the sub-panel and it should be connected to two 8' grounding rods sunk into the ground outside the building
I want the sub panel needs to have a main disconnect switch right there in the outbuilding, and I believe the panel/disconnect needs to be located within 6' of the outbuilding entrance (Is that right??).
So that's the plan. ANY comments are very welcome, and thanks in advance for sitting through another "dumb sub-panel question"!
Distance from my outbuilding subpanel to main 200 amp panel in house is a total of 150'
Wires to go through 2" diam underground PVC conduit with large diam. bends each end (It already exists and feeding a fish tape was a piece of cake!)
Outbuilding to be a "typical" small workshop, with table saws, band saw, drum sander, of which only one tool would be on at one time. Maybe 8 additional GFCI outlets and assorted lighting to be powered her as well.
Will install 100 amp sub-panel in outbuilding, controlled by 60 amp breaker at main panel power feed.
I believe that pulling 3 #4 copper wires and one #8 copper ground, all in exterior weatherproof casing will be the right mix of wires (THIS is what I am most uncertain about!! - Comments??)
I believe that the neutral and ground bar need to be disconnected at the sub-panel and it should be connected to two 8' grounding rods sunk into the ground outside the building
I want the sub panel needs to have a main disconnect switch right there in the outbuilding, and I believe the panel/disconnect needs to be located within 6' of the outbuilding entrance (Is that right??).
So that's the plan. ANY comments are very welcome, and thanks in advance for sitting through another "dumb sub-panel question"!