Discussion Starter · #1 ·
Hey guys, this house has a 200 amp service, a new breaker panel and done in 98% 12/2 wiring. Was there when I moved in. House ground is 4g to water main. Whenever I turn a light or set of lights on, other lights in the house dim slighty. Im not sure wether they come back to full brightness or stay dimmed just a little.

Meter plugged into wall outlet reads 120v. When lights are turned on the current actually went up to 121 or so.

Any ideas?

Just curious but is the nutral supposed to be in conact with the ground in the box? I dont have any idea if it is, im just asking.

I'm going to call an electrician later in the week but I'm wondering if you guys have any ideas.

thanks!
 

· Registered
Joined
·
47 Posts
Discussion Starter · #4 ·
Yes I meant in the panel.

We have not moved in yet so no sensitive electronics are hooked up right now. I will check the line voltage when my air compressor fires up. Is the loose neutral usually in the panel? or could it be an issue outside of house?
 

· Super Moderator
Joined
·
24,992 Posts
Loose neutral could be in panel, meter base, weatherhead connection, transformer connections.

If the compressor is 240 volts it won't trigger the issue as it doesn't use the neutral. You need to test with 120 volt loads.
 

· Banned
Joined
·
5,990 Posts
If the 3 thick wires that feed into your panel from the outside show the voltage imbalance then the problem is upstream of your panel. Measure them just upstream of the bolted connections.
Watch out for arc flash.
 

· Registered
Joined
·
47 Posts
Discussion Starter · #8 ·
Yes! :laughing:

If there's 5v across your bad neutral connection you'll have 125v on one side and 115v on the other.
5v at 10A might be enough to heat a bad bolted connection, if you have one of those IR meters.
This is the meter I have.

[URL="http://www.idealtruevalue.com/servlet/the-138498/Detail"]Ideal 61-310
[/URL]

So just to be sure, I put the + lead on one of the hot cables coming in and the - on the neutral, ground or other Hot?

Thanks. I've got my friend who is a electrician coming the end of the week. I just want to see if I can get this sorted.

-josh

p.s.
I had another guy tell me today that I can touch one of the hot cables coming in as long as I dont touch the other one.... i dont know what he's smoking but that dude is nuts.
 

· Banned
Joined
·
5,990 Posts
So just to be sure, I put the + lead on one of the hot cables coming in and the - on the neutral, ground or other Hot?
Plug in a 120v hair dryer somewhere. Check from the neutral to each hot lead.
More than probably a 1v difference between the nominal 120v readings means a high resistance neutral connection. The sum of both readings have to equal the incoming 240v, which will be 240v +/- 5% or +/-10%.
 