Measure the voltage between the two fuses. Should be 240 vac.

If you have voltage then you may have smoked the pump. Another thing to check is if there is a control box in the well then the capacitor(s) may have taken the brunt of the spike. If you cannot find any capacitors then more than likey the pump is smoked.
 