I did what you suggested and it is working. My unit looked like it had a power surge. The contactor was fried and I changed that, The power to the compressor was melted and I replaced that, I check the ohms on the compress and it checks out good. What elese could it be? If I disconnect the compressor wires and force the contactor on the fan runs, When the compressor wires are connected it trips the circuit breaker. Any suggestions
With all power OFF. And all wires removed from the compressor. When you check the compressor for continuity, check across R and C, S and C, and then R and S. R and S ohm value should equal the sum of the other 2 values.
Next, check from each of the compressor terminals to ground(one of the copper lines attached to the compressor is best), if anyone of them has continuity, the compressor is shorted to ground, and needs replaced. If n one of them do. Check that the run cap is not shorted to ground.
Its possible your compressor has a winding to winding short. That type of short can easily weld the contactor's contacts together, and heat it up enough to look like it was struck by lightening.