Hey I got a unit that I think is leaking freon. I thought i put 5.5 pounds in it last week. the tenant called 3 days later and said it was freezing up. I checked the filter, coils and everything inside and cleaned inside coils. when I put my guages on the low side it did appear to be low on freon. I am still not sure if I am reading the guages correctly. So I recovered all the freon. YUP 5.5 pounds! not one ounce short. But when I pulled a vacuum it would not hold. It would hold for 10 min or so and then drop a little. So to make a long story short I am thinking about using nitrogen, but I dont have a clue how to do this.

Any help ?
 

· Registered
Joined
·
201 Posts
Discussion Starter · #5 ·
Well I was going to start with a 100 and hope I could hear something. If not I will give it another 50 or so, or just see if it is holding. I have other stuff I could do while I wait an hour or so to see if it holds. If I do hear something, just hope I can get to it before I use 20 lbs of N1.
 

· Registered
Joined
·
368 Posts
Not sure you're going to hear a small leak. One option is to charge to 200-300 psi and go around with soap bubbles to find the leak. That will only work on fittings, but not the coil. The other is to add a 1/2 pound of charge, add the N1 to 200-300 psi and then use an electronic leak detector. If this is a small leak you may need to be pretty close with a detector. It seems leak detection is part science, art and luck.
 

· Banned
Joined
·
3,705 Posts
Not sure you're going to hear a small leak. One option is to charge to 200-300 psi and go around with soap bubbles to find the leak. That will only work on fittings, but not the coil. The other is to add a 1/2 pound of charge, add the N1 to 200-300 psi and then use an electronic leak detector. If this is a small leak you may need to be pretty close with a detector. It seems leak detection is part science, art and luck.

300psig??:eek: Thats a lot higher than some evap press burst test pressures.
 

· Registered
Joined
·
299 Posts
Well I was going to start with a 100 and hope I could hear something. If not I will give it another 50 or so, or just see if it is holding. I have other stuff I could do while I wait an hour or so to see if it holds. If I do hear something, just hope I can get to it before I use 20 lbs of N1.
You don't need a constant head (tank valve open). Pressurize to whatever pressure and close off the tank.

A leak anywhere will show on your gauges.

BTW, it's N2
 

· Registered
Joined
·
201 Posts
Discussion Starter · #10 ·
WOW! ok I went to 325 with out hearing anything. The pressure will hold for about an hour, and was holding when I left. I went around with soap with no luck. I was thinking I would go back in the morning to see if it was still holding. MY question is does freon leak faster then N2?
 