No, you need a neutral. You can not use the ground as a neutral otherwise its both an electrocution and potential fire hazard.
Hi,
I am trying to find out if I can connect a generator to a manual transfer switch without the neutral wire intact.
Here's the situation
I have a 7kw portalable gen set with a professionally installed manual transfer switch with L14-30 plugs on each side (2Hot, 1 Neutral 1 ground).
I just had a long (30+ hour outage) and found that some of my electronics really did not like the voltage variance that the generator provided.
So I picked up a Furman AR2330d voltage regulator used from a roadshow that just ended. This is a pro audio voltage regulator that is meant to plug between a generator and a stage amp setup and provide clean regulated voltage for electronics. It is supposed to have an 2 L14-30 (in and out's) on them. Someone altered the unit to have 2 L6-30 on it (2 hots and a ground).
I see they sell l14-30 to l6-30 adapters which simply omits the ground (not ground, the neutral).
------------
The question:
Can I used a couple of these adapters that omit the neutral wire between the generator and the transfer switch do I create a problem for myself given the neutral and ground are bonded at the circuit panel.
Thanks for your help. Merry Christmas.