Is it possible to have two 220V receptacles on the same circuit?

I currently have a 220 recep. in my garage for my welder. I would like to have one on the opposite side of the wall (exterior) for my compressor as well. They would never be used at the same time, if that matters.

I still need to check to see what size breaker the existing circuit is using.

Thanks!!!
 

·
Registered
Joined
·
41 Posts
Before doing anything be sure to consult your local electrical and building codes. High-voltage circuits are nothing to play with. You can have two outlets but you've gotta be careful not to exceed the amperage of the circuit breaker, outlets, and of course the installed wiring.

This may be a task better left to a licensed electrician.
 

·
Registered
Joined
·
1,802 Posts
Before doing anything be sure to consult your local electrical and building codes. High-voltage circuits are nothing to play with. You can have two outlets but you've gotta be careful not to exceed the amperage of the circuit breaker, outlets, and of course the installed wiring.

This may be a task better left to a licensed electrician.
High voltage? What do you consider high voltage?
 

·
Registered
Joined
·
259 Posts
Discussion Starter #6
I am going to consult an electrician on this. I was just curious how the 2 recepticals are hooked up, if they only have one set of lugs n the back.

FYI: the existing 220 recep. is on a 50 amp circuit.
 

·
UAW SKILLED TRADES
Joined
·
5,341 Posts
Your wiring likely is 6 awg copper protected by a 50 amp breaker...you would need to splice at the welder receptacle box and pigtail to the receptacle then on to the other outlet. However the air compressor may require a smaller breaker than the welder to be code compliant. Might be hard to meet code doing what you ask.
 

·
Registered User
Joined
·
6,520 Posts
Before doing anything be sure to consult your local electrical and building codes. High-voltage circuits are nothing to play with. You can have two outlets but you've gotta be careful not to exceed the amperage of the circuit breaker, outlets, and of course the installed wiring.

This may be a task better left to a licensed electrician.
Good advice for certain, but please remember that this is a DIY forum. When we can help someone we do, when we absolutely cannot...Then we send them to the pros.

As for the statements about high voltage subsequent to P&L's post:
220v certainly isn't high voltage but it'll kill you just as effectively.
 