We are building a tiny home in a remote location and will not have rural electric run and will rely on a generator.
Our local code guy has indicated it needs a "100A service" and seems to be hinging on IRC code. Under CH36, there is nothing I can see that would require a 100A service but does indicate the "conductor size" shall be sized for 100A.
it further runs through the calculations for sizing the service in which I am at approx 40-50A. Because a generator is most efficient at higher loads, installing a generator that is too big is not ideal.
Does anyone see something written in code that requires the actual service size to be 100A or more? I do understand that it appears I will have to install conductors for 100A though.