Hello,

I have a international confort producr COMFORTMAKER heater in my house. ANd noticed that burner is on for 10 second and off for 3 second and do continously. Think something wrong but do not know waht is going on. Sometime blower not on when in auto mode then hear clicking sound all the time then when I turn fan on then blower start. Is this thermo controller problem of some kind of sensor in the furnace.

Please Help
Thank you
 

· Roofmaster
Joined
·
3,732 Posts
We need the model number of the Furnace. Probably inside the furnace after you remove the panels so you can see the inducer fan and gas valve. Maybe to the left?

Make sure your flue and intake is clear, and your condensate lines and trap is clear.

Is your filter clean? How often do you change it?
 

· In Loving Memory
Joined
·
42,671 Posts
EAC's should be cleaned every 30 days, including the pre filters.

May have a problem with the exhaust and the pressure switch is opening and closing.
 

· Roofmaster
Joined
·
3,732 Posts
Clean your AC Evaporator coil. It sounds like you have an overheating condition, and this could be caused by dirt clogging up your coil.
 

· In Loving Memory
Joined
·
42,671 Posts
High limits don't reset in 3 seconds.

His coil may be dirty, but it is not the cause of the symptom he described.
 
  • Like
Reactions: jagans

· Registered
Joined
·
7 Posts
Discussion Starter · #9 ·
I agree to beenthere my coil is dirty but that caused this problem. When outside temperature is cold burner working continuously until it reached certain temperature (I set temp. to 68) and when outside temperature is warmer a lot of time burner turn on and off intermediately every 5-10 second for about 3 to 5 minute. Then blower never on then system off and keep doing this cycle until I switch fan auto to on then still burner kick on and off several times. The clicking sound is loud I can hear from the first floor where heater is located in basement.
 

· Roofmaster
Joined
·
3,732 Posts
Do you mean:

"I agree with Beenthere. My coil is dirty, but that is not what caused my current problem."


So you know your Evaporator coil is dirty, preventing proper airflow out of the furnace, but you are not going to clean it.

Beenthere might very well be correct, as I have followed his posts, and found him to be an excellent HVAC professional.

It is my opinion that dirt, debris, and corrosion are usually the culprits that cause the original problems in the first place, so getting your unit as clean as possible is always the starting point for logical deductive reasoning.

I think Beenthere will second me on this train of thought.
 

· Roofmaster
Joined
·
3,732 Posts
The water built up so high in your collector box due to lack of service that it flowed into your pressure switch. I would definitely replace it, after a thorough cleaning of your system, including your secondary heat exchanger. and all lines.

www.pexsupply.com
 

· Registered
Joined
·
7 Posts
Discussion Starter · #16 ·
I ordered pressure switch and cleaned pressure switch line and after 2 days later I noticed same problem again. Then I found water in the pressure switch line again. Checked in the morning found water again. Induced fan is hot and there should not be any mositure in it. Tube is connected top part of the induced fan and pressure switch has only one line comming from the induced fan. 11 years old furnace with electronic filter system and humidifier. I would like to know what happened on my furnace and how to fix?

Thanks
 

· In Loving Memory
Joined
·
42,671 Posts
Make sure the hose doesn't have a low spot in it on its path to the switch. next, look for a small hole at the port on the pressure switch. Make sure the hose is not covering it.
 