We are purchasing a home that will need to have all the siding (stained wood) and sheathing removed due to insect and woodpecker damage. We live in zone 4 and the walls are 2x6 on 16" centers. All the windows are going to be replaced as well. I am torn (monetarily) on closed cell spray foam but have concerns about settling on FG or Cellulose. The plan is insulation, 1/2 ply, housewrap, 1/4" XPS (R1.6) , then foam backed vinyl siding (R1.6). My first instinct is 3" of closed cell (R18) sprayed direct to back of drywall but thats a bit $$$ so am looking for any all ideas or flaws in plan. Thanks,
 

· Registered
Joined
·
37,499 Posts
I'd strongly suggest againt the insulated vinyl siding. Use a .045 high grade siding instead. The money saved could go toward having the spray foam done.

I've done a few home with the insulated siding, (customer insisted) and they all came back and report it made 0 differance in there heating and cooling cost.
There's still going to be air gaps where the seams are and around all the inside and outside corners,windows and doors like with any siding.

Sure hope your getting this house for a steal, a whole lot of work and money to do what your suggesting.
 
  • Like
Reactions: mae-ling

· Registered User
Joined
·
11,730 Posts

· Registered
House in Anglemont, B.C.
Joined
·
9,072 Posts
I think you will get far more bang for the buck if you use 5 1/2" Roxul batts in the cavities. Then cover that with a 1" or 1 1/2" foam board (usually EPS) and then your 1/2" plywood. Spray foam is quite costly.

I agree with Gary concerning the thermal bridging, which is VERY important to keeping your overall wall R rating high.
 

· Registered
Joined
·
7 Posts
Discussion Starter · #5 ·
Thanks for input all and the links GBR. Should it be foam then ply or ply then foam ? Putting the ply on the outside will make it easier for siding but not sure local code will allow without additional bracing on walls, at least the corners.
 

· Registered User
Joined
·
11,730 Posts
Where are you located?

Gary
 

· Registered User
Joined
·
11,730 Posts
Plywood sheathing before foamboard as per structural code. 1" of XPS (R-5) will warm your sheathing and prevent condensation there, up to 56%RH at 70* in the room. With just 1/4" (R-1.6), you are safe only to 48%RH. Local EPS may be rated at only R-3.5 per inch thickness, but I would get rid of the insects around the house first, as they love foamboard. If using ESP, install the housewrap exterior of it to control water intake/storage. If XPS, install housewrap first, tape the vertical joints in foam, and get the window/door flashing correct. http://www.buildingscience.com/documents/guides-and-manuals/gm-guide-insulating-sheathing

At annual low temp at 47*--- http://www.average-temperature.com/temps/MO/St Louis
your sheathing temp is at 49* with only R-1.6 f.b. or 52* with R-5.

Gary
 