Holy double stabs. You're full. Start a new sub panel off your main and move some stuff to the new panel. Check your loading as well and make sure you're not overloading your panel
Thanks. What's easier? A new sub panel or replace the current one? How do I best estimate my current load since obviously not everything is in use at the same time?
 

· Registered
Joined
·
585 Posts
Discussion Starter · #9 ·
Here's an interesting point. Below the main panel, there is a 240v plug. I guess I should figure out which breaker that's attached to (nothing is labeled to it) and see if I can run a longer wire out of the box. My table saw will be close to it anyways, can I just run a 12 gauge extension cord to it? Best case scenario, I could save 10 feet of run if I move the outlet and/or connect it directly.
 

· Registered
Joined
·
85 Posts
Depending on the configuration of the receptacle, and the requirements of your table saw.

If it's a 50A Breaker with a 50 Amp 6-50R (common welding plug) then you might want to change the breaker and the receptacle out to something more suitable. (6-30R or 6-20R) Depending on what your table saw requires.
 

· Registered
Joined
·
5,468 Posts
The simplest solution would be to double up on 2 smaller circuits If that's possible ?
That would free up some space in your panel.
Assuming you have the capacity amp wise ?
What are some of your smaller circuits ?
Have you done a load calculation ?
What size is your main breaker ?
 

· Registered
Joined
·
585 Posts
Discussion Starter · #13 · (Edited)
It appears that I have a 240v outlet labeled "GA 240v" already installed on a 50amp breaker. Great news!

Powermatic is recommending a 30amp circuit. Do I need to change the breaker to a 30amp?

The motor is rated as 3hp 230v 13amp. Can I run a 25 ft 10 gauge extension cord to the saw?
 

· Registered
Joined
·
11,194 Posts
I would remove the receptacle making it a junction box.
I would run conduit to the table saw location and mount a new receptacle and box within reach of the table saw power cord.
10 gauge wire. Change the breaker to 30 amps.

Using an extension cord in place of permanent wiring is a code violation.
 

· JUSTA MEMBER
Joined
·
20,351 Posts
I would suspect that a 50A circuit would void any warranty on the saw.

I am against using extension cords for several reasons, I would run a conduit along the wall from this area to a much closer to the saw area, and wire it anew, from a correct breaker to the saw.