The receptacle is for EV charging, it pull continuously 32 amp when charger connected.
Because that is 80% of 40A. Continuous loads (and plug-in loads) are required to limit to 80% of circuit ampacity.
I'm not going to be mad at you for not understanding this, because
this is really new technology. But.
That lump in the cord / thing on the wall is called EVSE (Electric Vehicle Supply Equipment) is not the charger. That's in the car. The EVSE's job is to tell the EV "The port you're plugged into has 24A available" (e.g. because it's a 30A circuit). The EV then draws 24A and no more. Plug in using the 120V dongle, then it will say "The port you're plugged into has 12A available". Etc.
Your car also has a hard max: if you plugged into a 100A EVSE and the EVSE said "You have 80A available" your car will draw 32A because that's its personal max.
A NEMA 14-50 socket is advertising that it has netural available (EVs don't use that)... and it has 50A available. The car you have
today happens to have a max of 32A, but what about your next car? Visitor car? You sell the house?
Hi, I wanted to install NEMA 14-50 receptacle in my garage for EV charging. Planning 40amp circuit. 40amp breaker, 8/3 wire (about 50 feet needed). My panel is in basement. Planning to get ESA permit myself (as home owner). My location is Ontario. Attached the image of the panel.
DO NOT run a 40A circuit to a NEMA 14-50 receptacle for EV charging. The 14-50 is advertising that it has
50A available not 40A. Most EVSE's will pull current like it's a 50A circuit (meaning pulling 40A continuously, and the breaker will probably tolerate this). Maybe this particular car doesn't, but you'll get a new model in a few years right?
In fact, I don't want to overload you with info, but the NEMA 14-50 is a source of high stupidity. A lot of people get fixated on it, because the car "comes with" a small "travel charger" meant for opportunity charging
on the road. The travel charger comes with a normal 120V plug and a NEMA 14-50 - why?
Because, NEMA 14-50 is found at RV campgrounds and sites.
They are not recommending NEMA 14-50 as an EV charge socket at home. In fact they sell alternate plug dongles for a huge variety of sockets.
All these are for sale, consult your manufacturer. The dongle has a micro-chip molded into the plug, that tells the car 15A, 20A, 30A or 50A. Per Code, it also monitors plug temperature and reduces or shuts off charge if the plug is getting hot.
In fact, Code requires you do a Load Calculation to determine the spare ampacity your home can dedicate to EV charging. By installing a 14-50
you are just presuming that number is 50 amps. It might be 30A, 20A or even 15A. You need to crunch those numbers.
Once you identify the ampacity, you pick the next smaller size out of 15, 20, 30 or 50. For you this is unlikely to be 50, so you'll be changing socket
amps anyway and thus buy a different dongle... so you might as well seize the opportunity and go with a 3-wire cable and socket, and save some money on your wire.
If you install a 14-30 or -50 you MUST install the neutral wire from the panel (because someone might plug an RV into that, and a missing neutral will fry most things that require 14-50). However the EV doesn't actually use the neutral.
1. My panel is 100amp, I have AC, electric dryer and stove. I don't think I will use all these - AC, stove and dryer at same time and only plan to charge EV at night most of the time. Can I manage with 100 amp panel? Any electrical code issue that I should aware in this case?
That gets sorted out in the Load Calculation. "No frickin' way" is my sense, but crunch the numbers for yourself.
There's a technology on the verge (available now for C$7000, will come down dramatically soon) which I call "Demand side management" but will probably be called "smart panels". This can schedule large loads so they don't combine to overload the panel. A readily available, but very "ghetto" option is to use a $30 Generator Interlock to lock out 2 of your loads so only one can be on at the same time. E.G. dryer and EVSE.
Then, the smaller of the two loads simply disappears from your Load Calculation. The side-by-side interlocks even allow an interlock
on each side of the EVSE breaker, which means it could be interlocked with
two other loads (dryer and range?)
2. Do I need a GFCI/AFCI breaker for this circuit? what is the code in Ontario/ESA?
I don't think so yet, but meet the other stupidity of plug-and-socket connected EVSEs.
EVSE's actually have a
second job, which is to be a GFCI to protect the car. They are smart GFCIs which will automatically "self-reset" several times to see if the fault cleared. If they have WiFi etc. capability, they will
tell you if they can't.
This means hardwired EVSEs (think: wall-mount units) will never need GFCI protection. Don't need a GFCI on a GFCI.
However, when an EVSE is connected plug/socket, the installer isn't installing an EVSE. They're installing a socket anything could be plugged into. Thus, they must comply with then-relevant local rules on GFCI.
3. Most of the area in the basement where wire goes is unfinished however close to panel it is finished area so I am planning to fish wire there (easy), would this finished area be a problem for inspection? do I need to cut open the drywall in that case for inspector to see wire?
No, they're not going to make you do that. Hey, did you know Canada has an amazing cable type called TECK? It was developed for mines, but apparently is widely used and solves many problems. It might even be allowed 75C thermal, granting 50A on #8 wire.