As shown in the photo, there is no main switch and no outside switch. I want to install a 200A circuit breaker/main switch so that I can turn it off when I turn on the generator.

Does anyone know what kind of circuit breaker should I buy for this pannel and where online can I find one?

BTW, do I need to tell the power company when I unplug the meter for a short amount of time? That is the only way to disconnect from the grid.

Thanks,

Alex
 

· Super Moderator
Joined
·
18,319 Posts
The first thing is that you do not have the training or protective equipment to pull a meter. It is also against the law in many areas.

You will need to check the panel label for a list of breakers that can be used in the panel. It may not be possible to add a main to that panel.
 

· Super Moderator
Joined
·
24,963 Posts
You need to tell more about the panel. It may not accept a main breaker. It could be a split bus panel and top half of the panel is consider the main even though it can have up to 6 breakers in it.

You need a proper transfer switch generator operation and it need to be permitted and inspected when installed.
 

· Electrical Contractor
Joined
·
1,995 Posts
Without knowing how much knowledge you have this is a beyond what most would consider DIY.
 

· Licensed Electrical Cont.
Joined
·
7,829 Posts
I agree with the others. I also get the impression that you are looking to backfeed from a generator without a transfer switch or interlock. This is a HUGE no-no.
 
  • Like
Reactions: micromind

· Registered
Joined
·
566 Posts
Without knowing how much knowledge you have this is a beyond what most would consider DIY.
Definitely sounds like you're in the territory of paying an electrician $100 to come out, examine your setup and give a recommendation, would be a good idea.
 

· Registered
Joined
·
301 Posts
My local POCO's proper protective equipment when pulling my 320a meter (400a service) is to pull the lever down then kind of look away and wince as you put the meter in or pull it out, lol.
The first thing is that you do not have the training or protective equipment to pull a meter. It is also against the law in many areas.

You will need to check the panel label for a list of breakers that can be used in the panel. It may not be possible to add a main to that panel.
 
1 - 8 of 8 Posts
This is an older thread, you may not receive a response, and could be reviving an old thread. Please consider creating a new thread.
Top