In yard "power post" - suggestions?

2918 Views 5 Replies 3 Participants Last post by  vsheetz
I am looking to install a post with 120V power outlets on it - in my yard. This will power a water fountain, two low voltage lighting transformers, and the occational power yard tool.

I understand the trenching and electric connection from a nearby building to the post - that's not where I am looking for info/suggestions - rather it's the actual outlets on the post itself. Here is what I am thinking, please toss out your thoughts and suggestions.

  • 4x4 treated post - 2' in the ground, 2' out of the ground - set in concrete.
  • Conduit exits the ground and goes up the post to outdoor single box #1 with duplex recept, then another short piece of conduit to outdoor single box #2 containing a dusk to down photo sensor, and yet another short piece of conduit to box #3 contain a duplex recept (switched by the photo sensor)
  • Each outdoor single box with duplex recept has a in-use weather cover
  • The low voltage lighting transformers are attached to the 4x4 post and plug into the photo sensor switched recepts - the fountain and the occational yard tool plug into the other (unswitched) recepts
Is there a better or differing way other than the multiple single boxes, recepts, and weather covers?

In-use recept cover such as this: http://www.mulberrymetal.com/MulberryBrochure.pdf

Thanks!
Vince
1 - 1 of 6 Posts
Assuming you're on 2008 NEC, your receptacles will need to be weather-resistant. These will have a WR on them. This includes the first one which must be a WR GFCI.

If not yet on 2008, the GFCI is still required. And I'm pretty sure the in-use weather cover is required by any code edition as well.
1 - 1 of 6 Posts