M1B series Miller furnace with Integrated Furnace Control board. Pic below.
Igniter w/flame sense glows to full brightness (30 sec warm-up period) after normal combustion air motor purge cycle, then a click from the board produces 24vac at gas valve, but only momentarily (1-second or less). Gas valve does not open.. no usual heavier relay clicking sound coming from the gas valve. At the same instant the 24v only "flashes" on my meter's LCD, the igniter powers off. No 6-seconds ignition trial time.
Repeats same two more times, then lockout. My guess is a bad IFC board (relay), because I had something very similar to this happen before (posted it in here) and you agreed with my diagnosis of bad control board, which it is was. However, this igniter w/flame sense is new to me and its resistance measured 174 ohms with its pigtails disconnected from the board leads that feed it voltage. I'm still thinking the board is bad, but also wondering about the combination igniter/flame sensor. Or maybe a bad igniter w/flame sense could shut down ignition attempts? I'm trying to find normal ohms range online for this igniter. No luck yet. Normal ohms range?
Not sure about the mounting part, but the round, spiral barrel (the element part) of the igniter in pic below is the same as the one on the furnace.
Problem is, I'm not sure how long after an initial ignition attempt, or two, it was when I checked its resistance. Maybe it was still warm which I'm guessing would yield higher resistance.
The pressure switch is lying down on upper shelf cuz I was checking it out.
Returning to the job on Monday and since supplier is not far from job, thinking I should check cold igniter ohms first, then pick one up if need be, along with a board. Good game plan? Bad game plan?
Igniter w/flame sense glows to full brightness (30 sec warm-up period) after normal combustion air motor purge cycle, then a click from the board produces 24vac at gas valve, but only momentarily (1-second or less). Gas valve does not open.. no usual heavier relay clicking sound coming from the gas valve. At the same instant the 24v only "flashes" on my meter's LCD, the igniter powers off. No 6-seconds ignition trial time.
Repeats same two more times, then lockout. My guess is a bad IFC board (relay), because I had something very similar to this happen before (posted it in here) and you agreed with my diagnosis of bad control board, which it is was. However, this igniter w/flame sense is new to me and its resistance measured 174 ohms with its pigtails disconnected from the board leads that feed it voltage. I'm still thinking the board is bad, but also wondering about the combination igniter/flame sensor. Or maybe a bad igniter w/flame sense could shut down ignition attempts? I'm trying to find normal ohms range online for this igniter. No luck yet. Normal ohms range?
Not sure about the mounting part, but the round, spiral barrel (the element part) of the igniter in pic below is the same as the one on the furnace.
Problem is, I'm not sure how long after an initial ignition attempt, or two, it was when I checked its resistance. Maybe it was still warm which I'm guessing would yield higher resistance.
The pressure switch is lying down on upper shelf cuz I was checking it out.
Returning to the job on Monday and since supplier is not far from job, thinking I should check cold igniter ohms first, then pick one up if need be, along with a board. Good game plan? Bad game plan?