Model number?I have a Lennox furnace with hot rod ignition. The gas valve do not open. The sequence of operations are Ok, like turning on fan, Hot surface ignitor begins getting hot, a click sound. However, the Gas Valve do not open. lights on the control board shows normal operation. The output on the transformer is 28 volts instead of 24 volts. Have tested two gas valves.
Thank you for your quick response.Model number?
Have you checked to see if the board is applying power to the valve after the igniter warmup period?
If you're sure you have gas, power is being applied to the valve but it doesn't open, valve is bad. Normally, verified with a manometer - see if there's any pressure output when power is applied, inlet pressure checked to verify there's normal gas pressure from the meter's regulator.
If no power is being applied to the valve, you have a problem in the electrical connection between valve and board, a safety like a pressure switch is cutting it off, or board is bad.
Does it throw any error codes?
Glad you got it going. Circuit boards have a response time and cannot react as fast as a fluttering pressure switch or some other problems but they do the best they can.Thank you, jmon, user_12345a, roughneck, and yuri. I really appreciate you guys helping me out. I learned a lot from your suggestions. So, the final disgnose was the faulty control board. I changed it and is working fine. The lessons learned for me.
a) Don't trust error codes from control board especially when it is signalling normal operations.
b) Normal sequence of operations until the opening of valve do not mean valve is bad.
c) The indication of 24 volts to the valve was for a fraction of a second. It should be longer.