Hi All. I am new to the board and this site. Super excited to be here.
I have been troubleshooting my York Furnace Model GY9S100C20UP11H.
About a month ago I replaced the York furnace Blower motor as it was very loud. Everything was working great and had no issues (york furance, heatpump, and propane). Then the other day I noticed that the heat pump condenser unit outside was running and then shutting off after about a minute or two and switching over to propane a lot. Temps were in the 40s and low 50s outside so this should not happen.
What I have determined is that whenever my heat pump comes on it starts to heat, but then the furnace blower motor will not come on. It then fails over to propane and the blower motor starts and heats the house.
If I place the thermostat in the fan on mode, the blower will not come on. Set it to heat and the above cycle occurs. Set it to AC and the same problem (Heat pump kicks in and runs but inside blower motor never starts). Set it to emergency heat and all works fine on propane.
Troubleshooting:
Have replaced the run capacitor
I have tested that there is varying resistance to the different fan speeds from high to low using my cheap old multi meter so it seems like the blower motr itself is fine.
No errors or flashing diagnostics code. Thermostat Green wire is supplying 24 volts to the board calling for fan.
The fan is connected to "Hi Cool" and I have verified that there is not120v current on the "Hi Cool" when the fan is set to on.
Any thoughts?
It looks increasingly like the control board is bad. Just want to check here before replacing it.
I have been troubleshooting my York Furnace Model GY9S100C20UP11H.
About a month ago I replaced the York furnace Blower motor as it was very loud. Everything was working great and had no issues (york furance, heatpump, and propane). Then the other day I noticed that the heat pump condenser unit outside was running and then shutting off after about a minute or two and switching over to propane a lot. Temps were in the 40s and low 50s outside so this should not happen.
What I have determined is that whenever my heat pump comes on it starts to heat, but then the furnace blower motor will not come on. It then fails over to propane and the blower motor starts and heats the house.
If I place the thermostat in the fan on mode, the blower will not come on. Set it to heat and the above cycle occurs. Set it to AC and the same problem (Heat pump kicks in and runs but inside blower motor never starts). Set it to emergency heat and all works fine on propane.
Troubleshooting:
Have replaced the run capacitor
I have tested that there is varying resistance to the different fan speeds from high to low using my cheap old multi meter so it seems like the blower motr itself is fine.
No errors or flashing diagnostics code. Thermostat Green wire is supplying 24 volts to the board calling for fan.
The fan is connected to "Hi Cool" and I have verified that there is not120v current on the "Hi Cool" when the fan is set to on.
Any thoughts?
It looks increasingly like the control board is bad. Just want to check here before replacing it.