Discussion Starter · #1 ·
Are those disconnects you put next to an HVAC unit mandatory code or just good practice? I have a theft problem on my ranch. This box makes it easy for crooks to avoid getting zapped. I am installing a small 2 zone mini-split. Nothing big. 30AMP. Water heater uses 30AMPs and does not have one of those switches. I can just as easily turn the breaker off to cut the power. Can I avoid installing one of these or will the inspector get a cow?
 

· Registered
Joined
·
37,499 Posts
Required by code here.
Put a lock on it.
Anyone with a screw driver could still still steal it without getting shocked.
 

· Registered
Joined
·
775 Posts
The disconnect has to be readily accessible and within site (50'). There are lockable ones. Explain the situation to your inspector to see if he'll allow a lockable disconnect out of site. Reference 440.14 exception No.1 (NEC 2011). It's not your situation at all but he might let it by.
 
1 - 6 of 6 Posts