Hi
I had an electrician come out to inspect my panel and provide an estimate for some additional circuits. He noticed that the HVAC condenser was connected to a 40A two-pole breaker with #10 wire (2x#10 w/G).
He stated that #10 wiring should be protected by 30A breakers, that a 40A circuit should use #8 wire, and that the present condenser wiring may be dangerous and a serious violation of the NEC.
The HVAC system is a recent upgrade/replacement for a 33-year-old system. The original condenser wiring was used to connect the new condenser. Sometimes the original 30A breaker has tripped.
The installer sent out a service technician who replaced the original 30A breaker with the current 40A breaker. It has not tripped.
The electrician recommended that I have another HVAC company inspect the HVAC wiring and determine what should be done. He would then be happy to provide an estimate of the cost to repair any sub-standard wiring.
The identification sheet on the condenser shows the following information:
LENNOX M/N: XC17-048-230-03
Electrical Rating: 1 PH, 60 HZ
Nominal Volts: 208/230 Min 197 Max 253
Compressor PH: 1, RLA: 21.8, LRA: 117
Fan Motor PH: 1, FLA: 2, HP: 1/4
Min. Ckt. Ampacity Amperage Minimum: 29.3
Max Fuse or Ckt. Bkr. Fusible/Coupe Circuit (HACR per NEC): 50
Can anyone determine from the above information if the condenser is not properly wired and/or not wired to Code?
Thank you for your time and expertise,
LynnX
I had an electrician come out to inspect my panel and provide an estimate for some additional circuits. He noticed that the HVAC condenser was connected to a 40A two-pole breaker with #10 wire (2x#10 w/G).
He stated that #10 wiring should be protected by 30A breakers, that a 40A circuit should use #8 wire, and that the present condenser wiring may be dangerous and a serious violation of the NEC.
The HVAC system is a recent upgrade/replacement for a 33-year-old system. The original condenser wiring was used to connect the new condenser. Sometimes the original 30A breaker has tripped.
The installer sent out a service technician who replaced the original 30A breaker with the current 40A breaker. It has not tripped.
The electrician recommended that I have another HVAC company inspect the HVAC wiring and determine what should be done. He would then be happy to provide an estimate of the cost to repair any sub-standard wiring.
The identification sheet on the condenser shows the following information:
LENNOX M/N: XC17-048-230-03
Electrical Rating: 1 PH, 60 HZ
Nominal Volts: 208/230 Min 197 Max 253
Compressor PH: 1, RLA: 21.8, LRA: 117
Fan Motor PH: 1, FLA: 2, HP: 1/4
Min. Ckt. Ampacity Amperage Minimum: 29.3
Max Fuse or Ckt. Bkr. Fusible/Coupe Circuit (HACR per NEC): 50
Can anyone determine from the above information if the condenser is not properly wired and/or not wired to Code?
Thank you for your time and expertise,