Installed a Venmar evo5 500 Hrv and tried to interlock to the furnace so the furnace blower comes on when the Hrv starts running when furnace thermostat set to auto. Thanks for the help.
 

·
Registered
Joined
·
15,540 Posts
check the manual.

should involve connecting an output from the hrv to the g terminal. do it wrong and it may backfeed through the stat to y and bring on the a/c if you have it.

running the fan with the hrv is wasteful and uncessary if it draws stale air from a dedicated vent.

This is a terrible way to install an hrv:



..if it's done that way i urge you to change it rather than doing an interlock. the furnace fan may draw something like 300-500w.

with the hrv pulling air directly from the house, not a return it will ventilate just fine without the blower running.
 

·
Banned
Joined
·
14,506 Posts
If you have no hook up and feel brave, you can always add a relay across the hrv blower motor which would activate the furnace blower. You would however have to open up the hrv and in doing so, void the warranty.

If you don't want to void the warranty probably the best thing to do would be to turn the furnace fan on with a differential pressure switch. You would mount the switch at the hrv and as it starts it causes a pressure difference in the hrv line which in turn activates the furnace fan.

The red and green wires would connect across the NO contact on the pressure switch and the positive/negative pressure lines would connect near to the hrv on the fresh air side.

 

·
Registered
Joined
·
13,975 Posts
Someone previously on here reported that their HRV had relay contacts on a terminal block, but no relay inside the machine. Apparently some models don't come with the relay. You'll have to follow the wires inside the HRV.

PS. Removing the out pipe of the HRV from the return duct, sealing the hole left behind, and letting it draw from inside the house, will allow the hrv to ventilate without the system fan.

Cheers!
 

·
Registered
Joined
·
13,975 Posts
My preference would be to use a relay in parallel to the relay for the HRV motor. (if no relay, then in parallel to the motor, adjusting the coil voltage to match) It would be the easiest, as no pressure tubes and taps. If you're not very good with electricity, the pressure switch might then be easier.

For the pressure switch, you'd need to measure the static differential that your unit will create. The switch will have to switch well below that, but higher then any parasitic static differential that will be present when the HRV is off, but the furnace fan is on. (should be zero, but the real world isn't perfect)

Cheers!
 

·
Banned
Joined
·
14,506 Posts
I like the relay idea better too, but if you want to go with a differential switch then you really should measure the differential pressure... but you need a meter for that. If you don't have one then this switch will most likely work (but I don't promise!)

The afs 145 or 222 are pretty universal and adjust from .05 to 12 inches... which is probably in your range.
http://www.kele.com/pressure/afs-series.aspx
 