I need to replace my roof. While I'm at it I'd like to install adequate attic ventilation. At the moment, the attic outlined in the picture below has just two small gable vents. I'd like a more modern system in which the air flows from the bottom of the attic to the ridge.
On the long edge (45 ft on the right side), there are no soffits. My roofing contractor says he can install a vented fascia at minimal cost. (Something like this, but not identical - basically it replaces the fascia board.) He can also install a ridge vent. (By the way, the roof pitch is 4:12.)
Note that to the left of the attic, the house has vaulted ceilings, so there is no attic. Will it be a problem if the only intake ventilation in the attic is from one side (i.e., the fascia vents)?
Another question is how to balance the intake and exhaust ventilation. According to the rule of 300, I need 374 square inches NFA, split evenly between intake and exhaust. A standard ridge vent (18 sq in NFA per linear foot) would provide 810 and the fascia vent would provide half that (405). Apparently one wants to avoid having more exhaust than intake because that can cause weather to be sucked in through the exhaust vent. So, what's the best way to make sure the system is balanced?
Obviously 810 square inches of exhaust is overkill. Is it possible to install a ridge vent on only half the length of the ridge? That would balance it exactly. If so - which half? Just in the middle, so there is an equivalent length of unvented ridge on either side?
On the long edge (45 ft on the right side), there are no soffits. My roofing contractor says he can install a vented fascia at minimal cost. (Something like this, but not identical - basically it replaces the fascia board.) He can also install a ridge vent. (By the way, the roof pitch is 4:12.)
Note that to the left of the attic, the house has vaulted ceilings, so there is no attic. Will it be a problem if the only intake ventilation in the attic is from one side (i.e., the fascia vents)?
Another question is how to balance the intake and exhaust ventilation. According to the rule of 300, I need 374 square inches NFA, split evenly between intake and exhaust. A standard ridge vent (18 sq in NFA per linear foot) would provide 810 and the fascia vent would provide half that (405). Apparently one wants to avoid having more exhaust than intake because that can cause weather to be sucked in through the exhaust vent. So, what's the best way to make sure the system is balanced?
Obviously 810 square inches of exhaust is overkill. Is it possible to install a ridge vent on only half the length of the ridge? That would balance it exactly. If so - which half? Just in the middle, so there is an equivalent length of unvented ridge on either side?