This used to be for a front porch light. We took out the light when we re-stucco'd and don't want to put it back. What I want to do is make it into an outlet. It is very well sheltered, so that's not an issue. If I could have an outlet here, I could plug in Christmas lights without duct-taped extension cords on the floor.

But what do I need to do for that conversion? I'm an electrical engineer and can do wiring, I just look at this and am not sure what I need. And I don't want to start tearing apart to examine, since I'd rather have a clue before starting to peel chunks of stucco off.

Is this an insert from the porch light, mounted into a blue box nailed to the stud? Or is the gray part the box nailed to the stud and the threaded piece sticking out is from the light?

Thanks!
 

· Super Moderator
Joined
·
18,318 Posts
The round hole is an adapter ring from a square box. The threaded stud is to mount the fixture.

You would need to switch the ring to a device ring and provide gfi protection.
 

· Super Moderator
Joined
·
24,961 Posts
Being as this used to be a porch light I suspect it is up high. Does it need a bubble cover. I thought only receptacles within a certain distance of the ground needed them. In Canada receptacles 2.5 meters above grade do not need GFCI
 

· Registered
Joined
·
11,194 Posts
Assuming way up high and deep in an over hang is a damp location (not wet), the in use cover is not required. While it may be used, the older flat type exterior cover is fine.

I am not aware of any height exception for GFCI protection on exterior receptacles in the NEC. The GFCI should be the weather resistant type.
 

· Banned
Joined
·
17,162 Posts
What if they go with the round cover that is used to run conduit for lights, etc, and then place a standard Single gang box to the side of the old light box. The only other in-use covers that are out there, are for the 4" boxes.

The one in use cover that manufacturers never think to have made, are for the round boxes.
 

· Super Moderator
Joined
·
24,961 Posts
That actually looks like it might be a square box with a round plaster ring like this.

If that is true then one of these will work and accept the receptacle and any type cover you want.

 