Hello all.
I am in the planning stages for adding lights and receptacle to my finished garage.

I have a surface mounted sub panel. For the lights I can go one of two ways. I can run conduit to the switch location then conduit up into the attic and run romex from light to light. This could be simpler, cheaper and neater. How do I go through the drywall? Do I put a junction box in the attic to terminate at?

The other option is to surface mount conduit to every connection.

Thank you.
 

· Registered
Joined
·
350 Posts
Run / attach the conduit to a junction box, and then put a clamp for the romex, not a problem.

You should to run a green ground wire in the conduit along with the hot and neutral so the romex has a nice solid ground. technically not necessary, as the conduit acts as a ground, but a good idea.
 

· Registered
Joined
·
350 Posts
I was thinking THHN in the conduit. That cool doohicky would work if running NM in the conduit, but no room for wirenuts!
 

· Licensed Electrician
Joined
·
4,352 Posts
Show that connector begs two questions. Are you allowed to run romex in conduit? If not how do you make the junction without a box?
As long as the pipe isn't outside.
 
  • Like
Reactions: TTW and electures

· Registered
Joined
·
6,039 Posts
Stub the EMT into the attic and put a romex to EMT connector on that end.

This fitting is designed for conduit to Romex transition. I have used this connector to transition to metal flex before, but I do not think the connector is listed for the purpose.

There are no connections here. Just Romex through the conduit and then out the end of this connector.
You could use a regular connector and bushing instead if you prefer.
If you garage is finished, why do you want to surface mount the wiring method for lighting and receptacles?
If you have drywall up, you should have everything recessed and and hidden from site.
 

· Super Moderator
Joined
·
11,052 Posts
If you are running individual wires in the conduit, you have to transition to a box for the connections.
It could be right at the ceiling, and just poke the romex into a box with the approved connector.
 

· Registered
Joined
·
350 Posts

· Licensed Electrician
Joined
·
4,352 Posts
Didn't like the answers you got in the other thread?
 