Hi folks,

First time on this forum so I appreciate your help.

I would like to install smart light switches but there was never a neutral wire run in my house. I opened the panel and I think I know where I need to install the wire. I have circled it below, is this correct?


Electricity Circuit breaker Electronic engineering Electrical wiring Electronic component



So if this is where I install this single wire I have a question or two:


Many thanks for your help.
 

· Naildriver
Joined
·
24,749 Posts
You have neutrals run throughout your house, as evidenced by the white wires. The only problem is that the power enters the fixtures rather than the switch boxes. The electricians used a switch loop to energize and control the lights, making no neutral at the switches apparent.

No you can't run a single wire outside the casing of the cable. It must be contained in the sheathing. It would be best to search for a smart switch that doesn't require a neutral. Today's codes require xx-3 cables run from fixtures to switches with the white wire capped off for such a use as yours.
 

· Registered
Joined
·
5 Posts
Discussion Starter · #6 ·
Okay, just dumbing this down like I'm 5.

I have a black wire, white wire and the bare ground wire going directly to the panel. For the smart switch my neutral wire is just the white wire?

Just as long as there is no fixture between my main switch and power source I'm good?
 

· Registered
Joined
·
5 Posts
Discussion Starter · #7 ·
You have neutrals run throughout your house, as evidenced by the white wires. The only problem is that the power enters the fixtures rather than the switch boxes. The electricians used a switch loop to energize and control the lights, making no neutral at the switches apparent.

No you can't run a single wire outside the casing of the cable. It must be contained in the sheathing. It would be best to search for a smart switch that doesn't require a neutral. Today's codes require xx-3 cables run from fixtures to switches with the white wire capped off for such a use as yours.
Sorry, I should have quoted your post:

Okay, just dumbing this down like I'm 5.

I have a black wire, white wire and the bare ground wire going directly to the panel. For the smart switch my neutral wire is just the white wire?

Just as long as there is no fixture between my main switch and power source I'm good?
 

· Naildriver
Joined
·
24,749 Posts
OK, power comes from your panel via the black wire attached to the breaker. It is returned via the white neutral wire. Those wires go to the light fixture in the ceiling. If you had no switch, the light would stay on all the time because there is no control. Installing a switch loop, incorporating the white (taped black) and black wires to the switch make and break the connection allowing you to control your light. There is NO neutral at the switch if all you have is two wires.

Font Parallel Circle Gas Auto part
 

· Registered
Joined
·
5 Posts
Discussion Starter · #11 ·
You have neutrals run throughout your house, as evidenced by the white wires. The only problem is that the power enters the fixtures rather than the switch boxes. The electricians used a switch loop to energize and control the lights, making no neutral at the switches apparent.

No you can't run a single wire outside the casing of the cable. It must be contained in the sheathing. It would be best to search for a smart switch that doesn't require a neutral. Today's codes require xx-3 cables run from fixtures to switches with the white wire capped off for such a use as yours.
OK, power comes from your panel via the black wire attached to the breaker. It is returned via the white neutral wire. Those wires go to the light fixture in the ceiling. If you had no switch, the light would stay on all the time because there is no control. Installing a switch loop, incorporating the white (taped black) and black wires to the switch make and break the connection allowing you to control your light. There is NO neutral at the switch if all you have is two wires.

View attachment 735097
Only if you're sure the white is a neutral that goes to the panel. Is the white connected to the switch? If so, it's not a neutral; it's a switched hot wire.

Thanks.

I will install it exactly like this:

Line Font Parallel Slope Auto part


This is for the Kasa 3 way dimmer. In this diagram I'm only seeing black/white/ground coming from power source.

This is so confusing because I'm used to opening the box and seeing 2 or 3 neutral wires connected together. I would then connect all my white wires together and that would be my neutral, I think.

So for this install should I only need my white/black and ground going back to the panel?
 

· Registered
Joined
·
2,251 Posts
Don't worry about the wire from panel. It likely goes several places before the light such as receptacles. You have the neutral at the light already. Light to switch is your only concern.
You may possibly can run a cable from a nearby receptacle to switch.
 

· Registered
Joined
·
5 Posts
Discussion Starter · #13 ·
Don't worry about the wire from panel. It likely goes several places before the light such as receptacles. You have the neutral at the light already. Light to switch is your only concern.
You may possibly can run a cable from a nearby receptacle to switch.
Okay, many thanks.

At this point, I think I will try to get an electrician in to help me with this. I would really like to get these TP-Link units in, instead of the Casetas.
 

· Registered
Joined
·
2,906 Posts
I want to know where all these DIY guys get the software to draw such nice diagrams.
I dare say most are borrowed from PDFs and other sites. I've done a few on my own with photos and paintdotnet and it is tedious.

EDIT: Added link.
 

· Registered
Joined
·
8,176 Posts
Okay, just dumbing this down like I'm 5.
"Hire... an... electrician" :)

Seriously OP, you are "bouncing off the walls" here because you are way, way, way out of your depth.

I mean it's not monstrously hard, but it's like if someone handed you a Piper Cub airplane and said "have fun". Very docile and novice-friendly airplane. You can jab at it by trial and error and get it moving down the runway and lifted off, but in the next 4 hours you ARE going to die LOL.

You've got a smart switch and your brain said "This is a consumer product meant to be DIY'ed. Surely that MUST mean it will be super easy to install" and so you're expecting a low difficulty level.

Well, no. There are at least 2 different ways to wire a plain switch and 5 ways to wire a 3-way switch. You don't even have the vocabulary to say which one you have... and there are lots of complications you can run into.

So yeah. Flight school bruh.


I have a black wire, white wire and the bare ground wire going directly to the panel. For the smart switch my neutral wire is just the white wire?
Not necessarily. All cables are made either black-white, or black-white-red. That reflects how the cables are manufactured, it provides no indication whatsoever of the actual function of those wires. Code requires very minimal markings, but those are usually ignored, and in any case only inform people with basic skills in place. So one of those "complications" is recognizing a mis-marked switch loop.

Thanks.

I will install it exactly like this:
NO. Don't install anything "exactly" like anything. You have to identify what you have, and then see which method is applicable. No replacement for that.

I want to know where all these DIY guys get the software to draw such nice diagrams.
Most of them are copying pro diagrams made by a manufacturer. However Adobe Illustrator does a bang-up job of making an amateur drawing look semi-pro. I'm sure there are open-source alternatives.
 