Discussion Starter · #1 ·
Do I simply need to purchase a multi-thousand dollar voltmeter?

The ones at home depot only go up to 10-20A maximum. The ones on ebay are even worse :wink:

I am hoping to plug this HP E7681-63001 PDU into my 30A dryer receptacle and then plug some computers into that - a mini data-center so to speak. But first I need to determine the voltage, because it will determine whether or not I can plug in 7,200 Watts worth of computers (if 240V) or 3,600 Watts worth of computers into one outlet, correct?
 

· " Euro " electrician
Joined
·
5,369 Posts
Typical North Américaine Dryer receptale are wired for 120/240 volts and there is two conferation of three wire and four wire verison and the power strip you set up in the link.,

That if have 4 wire then it is no issue with it due you can able run balnced load without issue.

Can you tell us if you have three or four wire receptale at the dryer location ?

Merci,
Marc
 
  • Like
Reactions: darkaspitch

· In Loving Memory
Joined
·
42,671 Posts
If your dryer circuit is 30 amps. You still can't draw 7200 watts continuous..
 

· Registered
Joined
·
10,407 Posts
Do I simply need to purchase a multi-thousand dollar voltmeter?

The ones at home depot only go up to 10-20A maximum. The ones on ebay are even worse :wink:?
The cheapest voltmeter will do. The 10 to 20 amp maximum is for measuring actual current usage or flow (in amperes) which you really do not need to do for this project.

The dryer receptacle has the same 120/240 volts as your breaker panel and the voltage won't change by more than two or three, unless there is a loose connection (a defect) which needs to be fixed before you use the circuit for anything no matter how small.

If the dryer circuit is wired with 10 gauge wire then you can draw two allotments of up to 24 amps (2900 watts) each on a continuous draw basis.

You need to make up a power load center (a kind of subpanel) with a cord and matching plug for the dryer receptacle, and a box with a number of breakers not exceeding 20 amps each, and 120 volt receptacles either in the same box or in additional boxes. Correction, the Power Distribution Unit linked to above is the load center; you don't need to make anything yourself. However, in the U.S. no one standard 15-20 amp receptacle may have access to more than 20 amps so if the PDU doesn't have built in breakers limiting each receptacle to 20 amps then the circuit into which you plug it has to have a 20 or fewer amp breaker.

If the dryer receptacle has only three prongs you will need to ground your load center. This may be done for a portable load center by adding a ground wire from the load center box strung to any known ground. (If you substitute a 4 prong dryer receptacle and the feed cable does not have a ground, then you need to replace the feed cable with one with a 4'th conductor for ground.)
 
  • Like
Reactions: darkaspitch

· You talking to me?
Joined
·
7,551 Posts
hey everybody; the ebay site linked is a Canadian site and the PDU shown is apparently straight 240 volt (3 wire twist lock receptacle)



are you in Canada darkaspitch? The ebay site you used is the Canadian extension of eBay and I see some receptacles on that strip that look a bit odd compared to US styles.

Regardless, you will not be able to pull 7200 watts continuous. That is the max load available on a 30 amp 240 volt circuit and you will not be able to max it continuously, You need to reduce the load to 80% for a continuous use.
 

· Electrician
Joined
·
1,404 Posts
That looks like a 240V device, I don't see how you would get 120V out of it. Nap the two plugs by themselves look like they are 240V/15A plug, the other plugs look like regular 15A plugs but I don't see how that is possible.
 

· You talking to me?
Joined
·
7,551 Posts

· Registered
Joined
·
5,468 Posts
Why dont you use a clamp on amp meter ?
such as this -
If you search around you could find a plug in version,
Not too expensive, and the safest way to do it.


Do I simply need to purchase a multi-thousand dollar voltmeter?

The ones at home depot only go up to 10-20A maximum. The ones on ebay are even worse :wink:

I am hoping to plug this HP E7681-63001 PDU into my 30A dryer receptacle and then plug some computers into that - a mini data-center so to speak. But first I need to determine the voltage, because it will determine whether or not I can plug in 7,200 Watts worth of computers (if 240V) or 3,600 Watts worth of computers into one outlet, correct?
 

Attachments

· Registered
Joined
·
15 Posts
Discussion Starter · #12 ·
If your dryer circuit is 30 amps. You still can't draw 7200 watts continuous..
I don't plan on it... I was just mentioning that is the total amount available.

I was going to plug a voltmeter into the outlets to determine if it was 120 or 240V (or 3,600 or 7,200 watts maximum...)

I plan on only using ~75% continuous load.
 

· Registered
Joined
·
15 Posts
Discussion Starter · #13 · (Edited)
The cheapest voltmeter will do. The 10 to 20 amp maximum is for measuring actual current usage or flow (in amperes) which you really do not need to do for this project.

The dryer receptacle has the same 120/240 volts as your breaker panel and the voltage won't change by more than two or three, unless there is a loose connection (a defect) which needs to be fixed before you use the circuit for anything no matter how small.

If the dryer circuit is wired with 10 gauge wire then you can draw two allotments of up to 24 amps (2900 watts) each on a continuous draw basis.

You need to make up a power load center (a kind of subpanel) with a cord and matching plug for the dryer receptacle, and a box with a number of breakers not exceeding 20 amps each, and 120 volt receptacles either in the same box or in additional boxes.

If the dryer receptacle has only three prongs you will need to ground your load center. This may be done for a portable load center by adding a ground wire from the load center box strung to any known ground. (If you substitute a 4 prong dryer receptacle and the feed cable does not have a ground, then you need to replace the feed cable with one with a 4'th conductor for ground.)
...swooooooosh.... (way over my head) but thanks!

Edit: after re-reading, I think I may have got some of it!?

So I can plug a 10A voltmeter into any wall receptacle and it will give me a proper reading?

And basically what you are saying is... that if my entire apartment is 120 volts, then the dryer receptacle is most likely 120 volts as well..?

There are two dryer plugs actually, so I assume it is 120 volts coming out of there... darn.
 

· Registered
Joined
·
15 Posts
Discussion Starter · #15 ·
That looks like a 240V device, I don't see how you would get 120V out of it. Nap the two plugs by themselves look like they are 240V/15A plug, the other plugs look like regular 15A plugs but I don't see how that is possible.
It is indeed a 240V device.

Which is why I need to know if my dryer receptacle is spitting out 120 or 240 volts before I purchase it.
 

· Registered
Joined
·
15 Posts
Discussion Starter · #16 · (Edited)
Typical North Américaine Dryer receptale are wired for 120/240 volts and there is two conferation of three wire and four wire verison and the power strip you set up in the link.,

That if have 4 wire then it is no issue with it due you can able run balnced load without issue.

Can you tell us if you have three or four wire receptale at the dryer location ?

Merci,
Marc
Ok guys here is an update...

This is what my dryer plug and receptacle look like:





Also I am 99% positive now that my dryer receptacle is spitting out 240 volts... because it has 2 * 30 amp breakers dedicated to it.

When you combine a 120 volt source with another 120 volt source, the voltages are added together, correct?

Can anybody tell me what the maximum wattage of this receptacle would be? (If there are 2 30A breakers dedicated to it, probably at 120 volts each..?)

According to this picture of the PDU I have in mind however... there are only 3 prongs on the plug, so I guess this will not work then?
 

· Registered
Joined
·
1,802 Posts
The dryer recep is likley 240 volt - even if the rest of your apartment is 120v. The question asked previously is valid - do you have 3 or 4 wires to the recep for the dryer? A picture of the recep would help too.

Please don't take this wrong, but as it seems you are pretty unfamilier with electricty and wiring, I don't think you should be poking around with a meter.

A Google of 240 circuits, dryer connections, wiring, etc will show you how they work, are wired, and what the differing receps look like. If 240 volt, you will find 240 volts across two of the connections.

Once determined to be 240v, how are you going to get the recep changed to accept the L6-30 plug of the PDU? In an apartment you need to have the landlord approve and likely have it done, by an electrician.
 

· Registered
Joined
·
1,802 Posts
Ok guys here is an update...

This is what my dryer plug and receptacle look like:





Also I am 99% positive now that my dryer receptacle is spitting out 240 volts... because it has 2 * 30 amp breakers dedicated to it.

When you combine a 120 volt source with another 120 volt source, the voltages are added together, correct?

Can anybody tell me what the maximum wattage of this receptacle would be? (If there are 2 30A breakers dedicated to it, probably at 120 volts each..?)

According to this picture of the PDU I have in mind however... there are only 3 prongs on the plug, so I guess this will not work then?
Appears you do have a 120/240 dual voltage dryer circuit, with ground. Suggest you next contact your landlord regarding changing the recept to accomodate the PDU.
 

· Registered
Joined
·
15 Posts
Discussion Starter · #20 ·
Appears you do have a 120/240 dual voltage dryer circuit, with ground. Suggest you next contact your landlord regarding changing the recept to accomodate the PDU.
I am the landlord :S

And yes, I am quite inexperienced when it comes to electricity. I only really know computers.

Now we're getting somewhere though....

So the receptacle in my apartment can be either 120 or 240 volts, correct? Depending on which prongs the device decides to pull from.

And there is a grounding wire (rounded prong) as well?

The PDU is rated at 240V and 30A ... It only has 3 prongs, which (I assume?) are a positive, negative & grounding wire?

Are there no adapters out there that could simply plug into the 4 pronged 120/240V receptacle and give me a straight 240V 30A receptacle? Something like this perhaps??