Aren't all new dryers 4-wire now??
It's not the dryer that makes it a 3-wire or 4-wire. It's the feed/receptacle at the house.
The backs of most dryers haven't changed in probably 40 years.
 
  • Like
Reactions: Jim Port

·
Licensed Electrical Cont.
Joined
·
7,829 Posts

·
Registered
Joined
·
1,461 Posts
I seriously hope this isn't from Maytag. I ran out of fingers and toes to count the number of errors even if hardwiring the dryer is legal. The only good thing, this guy won't be back feeding through his dryer outlet.
 

·
Super Moderator
Joined
·
17,304 Posts
They say to use a 3/4 connector and then install a 1/2"?

That screw was tightened on the wire? Are you kidding me. You could watch it moving under the screw head.

Why did we cut the ground off?

Someone at Maytag needs their butt kicked for not checking this crap.
 

·
Super Moderator
Joined
·
17,304 Posts
Just followed up up with Maytag customer support chat to make them aware of the issue.
 
  • Like
Reactions: Jump-start

·
Super Moderator
Joined
·
23,953 Posts
For the DIYs who don't know can you point out all the issue with this video.
I'll start with the obvious ones.
1. NEVER cut off the ground wire.
2. The cable clamp should be clamping the sheathing not the wires after they come out of the sheathing.
 

·
JOATMON
Joined
·
17,364 Posts
This is what I use exclusively for stripping #12 and #14 wire:



But only because I'm not adept enough at using these: :cool:

That is similar to what I use....

If you are having to rotate the strippers 2-3 times around the wire and then yank on it like your trying to open a Xmas present, I think you might be using the wrong strippers....kinda reminded me of the guy who kept getting zapped
 

·
Registered
Joined
·
249 Posts
If you are having to rotate the strippers 2-3 times around the wire and then yank on it like your trying to open a Xmas present, I think you might be using the wrong strippers....kinda reminded me of the guy who kept getting zapped
Yeah, and it's dangerous. You're far more likely to get nicks in the wire doing it that way. And that's what causes heat and fires, probably at least as much as bad wire nut connections.
 

·
Registered
Joined
·
112 Posts
They say to use a 3/4 connector and then install a 1/2"?

That screw was tightened on the wire? Are you kidding me. You could watch it moving under the screw head.

Why did we cut the ground off?

Someone at Maytag needs their butt kicked for not checking this crap.

It's tightened on the wire because it's a Romex connector... Makes total sense.
 

·
Registered
Joined
·
2,512 Posts
Discussion Starter #18
For the DIYs who don't know can you point out all the issue with this video.
I'll start with the obvious ones.
1. NEVER cut off the ground wire.
2. The cable clamp should be clamping the sheathing not the wires after they come out of the sheathing.
For beginners:

3. Use the correct rated clamp for FMC/Greenfield, not NM clamp.

4. Directions say solid only, not stranded

5. Incorrectly torqued terminals

6. 4 wire connection was turned into a 3 wire.
 