Discussion Starter · #1 ·
Hi there.

My bath room has (from left to right) a sink, toilet, and a tub. The vent pipe is connected to the sink (1.5") and runs out the roof. No other vents. As I understand it this makes it a wet vent. What I'm wondering is if I can add a wash box (for washing machine) in between the toilet and the sink. Sink and tub are only a few feet apart. Wash box will be added on other side of wall. Any advise very much appreciated. in ohio. Thanks.
 

Attachments

· Registered
Joined
·
558 Posts
By any code I'm aware of, what you have there is a properly vented lavatory and an unvented toilet and tub. A wet vent is supposed to be 2" minimum, and to be correct the tub drain would have to wye off the toilet drain (3"x 2" wye rolled above the centerline of the 3" run), and the lav drain/wet vent would have to wye off the tub drain (2" wye rolled above the centerline of the horizontal tub drain).

I think a 2" vent stack serving a laundry in the location you've decribed wouldn't hurt anything. That would make the 2" stack the (sort of/default) faux wet vent for the toilet and tub. Some jurisdictions (like mine) do not allow a washing machine drain to be used as a wet vent; some do.
 

· Registered
Joined
·
1,169 Posts
is there any thing else draining into the 3 inch pipe thru out the whole house
 

· Registered
Joined
·
74 Posts
Discussion Starter · #4 ·
By any code I'm aware of, what you have there is a properly vented lavatory and an unvented toilet and tub. A wet vent is supposed to be 2" minimum, and to be correct the tub drain would have to wye off the toilet drain (3"x 2" wye rolled above the centerline of the 3" run), and the lave drain/wet vent would have to wye off the tub drain (2" wye rolled above the centerline of the horizontal tub drain).

I think a 2" vent stack serving a laundry in the location you've decribed wouldn't hurt anything. That would make the 2" stack the (sort of/default) faux wet vent for the toilet and tub. Some jurisdictions (like mine) do not allow a washing machine drain to be used as a wet vent; some do.
I'm starting to think there was no inspections when this house was build (2004) ha. Anywho...Sorry for the crude drawling..yes the lav is wyed off the toilet. So if I 90 down the trap arm (with no san tee & vent) am I asking for trouble?
 

· Registered
Joined
·
1,169 Posts
put a 3 inch wye on its side turn a 3 inch 90 up into wall cavity under floor reduce to a 2 inch then run up through floor into wall cavity then plumb it in as picture and the off top of t where wash machine trap is reduce to 1 1/2 vent run up above height of the sink a foot or more then run over to sink vent and ty into it with a sani t. now if i remember correctly the vent size should be 2 inch or larger the rest off the up off the t where sink vent and wash machine vent ty in together, but a 1 1/2 will work
http://newhome.michaelwardonline.com/wp-content/uploads/2009/08/New-House-117.JPG

and get ready to hear how this is not code but it will work
 

· Registered
Joined
·
558 Posts
I'm starting to think there was no inspections when this house was build (2004) ha. Anywho...Sorry for the crude drawling..yes the lav is wyed off the toilet. So if I 90 down the trap arm (with no san tee & vent) am I asking for trouble?
Yeah...that's asking for trouble. Run the vent up through the roof in 2". Then you'll be about half a step closer to code compliance.
 
1 - 7 of 7 Posts