how many runs can I have in a 1 inch pipe. all #12g wire? I know I can run 29 #12 but don't I need to start derating the wires after a certain number of hots?
 

·
Super Moderator
Joined
·
8,875 Posts
How long is the pipe?
 

·
Licensed Electrical Cont.
Joined
·
7,829 Posts
You can have 9 (nine) #14, #12 or #10 CCC (current carrying conductors), which includes neutrals, before you even have to consider derating.
 

·
Registered
Joined
·
14 Posts
Discussion Starter #4
I have 26 #12 wires in a 1inch conduit which 12 are hot and 12 neutrals. there is a 1 inch emt connection to the panel that runs to an Lb and a 1 inch flex to a junction box. the pipe and flex are both about 3 feet in length.
 

·
Licensed Electrical Cont.
Joined
·
7,829 Posts
That's a LOT of wire in that pipe. That is the maximum fill.
Who laid that out?
 

·
Registered
Joined
·
843 Posts
I have 26 #12 wires in a 1inch conduit which 12 are hot and 12 neutrals. there is a 1 inch emt connection to the panel that runs to an Lb and a 1 inch flex to a junction box. the pipe and flex are both about 3 feet in length.
I used to pull THHN # 12 for machine tools that were laid in race ways. 26 wires in a 1” pipe is a lot to say the least.
 