If you are trying to plug into a 4 wire dryer receptacle, it will not work.
You need to run a new circuit to match the welders requirements.
 

· Registered
Joined
·
107 Posts
Welder circuits are "special". See NEC 630. You might be able to use the dryer outlet, but you need to determine the current requirements and the duty cycle of the welder to see if your wire size and breaker are adequate for the welder. You can make the plug match by changing either the outlet or the plug, but you need to review NEC 630 for wire size and breaker requirements. Also, if the breaker size needed exceeds the NORMAL breaker for the wire size for a branch circuit, the outlet MUST be labeled "Welder Only".
 

· Licensed Electrical Cont.
Joined
·
7,829 Posts
Also, if the breaker size needed exceeds the NORMAL breaker for the wire size for a branch circuit, the outlet MUST be labeled "Welder Only".
Don't get me wrong, I am NOT an advocate of applying Art.630 to a residential setting, but can you tell me where in the code book you find this "welder only" label requirement?
 

· Registered
Joined
·
2 Posts
Discussion Starter · #7 ·
Home 220/240 volt

This plug is in my garage the washer dryer are in the house the receptical is 4 wire green white and 2 red the welder is 220/240 single phase greem white and black. The braker is 50 amp my old house the dryer was 3 wire 30 amp braker and worked fine. Will that help. And i live in west sac. Ca. If you want to send a price to do the work if you can not help this way.
Thanks
very much
dave
 

· Semi-Pro Electro-Geek
Joined
·
3,404 Posts
This plug is in my garage the washer dryer are in the house the receptical is 4 wire green white and 2 red the welder is 220/240 single phase greem white and black. The braker is 50 amp my old house the dryer was 3 wire 30 amp braker and worked fine. Will that help. And i live in west sac. Ca. If you want to send a price to do the work if you can not help this way.
Thanks
very much
dave
Install a 4-wire dryer cord on the welder. Connect the green wire to the welder's ground, the red and black wires to the welder's hot terminals (which might be color coded red and black or red and white, doesn't matter). Do not use the white wire from the dryer cord; tape it off or wire nut it.
 

· Scared Electrician
Joined
·
715 Posts
Don't get me wrong, I am NOT an advocate of applying Art.630 to a residential setting, but can you tell me where in the code book you find this "welder only" label requirement?
now thats a good question pete. Enlighten us
 