Just bought a house and i saw that the bathroom circuit is on a 20 amp breaker,it is wired with 14 wire including the lights,what do i need to do the house was built under 1975 codes? Is this legal in Florida orange county?
 

·
Scared Electrician
Joined
·
715 Posts
it was never code to allow 14ga wire on anything bigger than a 15amp breaker. All modifications must be done to the newest code.
 
  • Like
Reactions: julie112

·
Lic Elect/Inspector/CPO
Joined
·
369 Posts
This never code, but it isa reason codes get changed.
Back in 1975 bathrooms could be on a 15 amp circuit. As people move in and hairdryer are used the 15 amp breaker trips, so the HO puts in a 20 amp cb to solve the problems, even though it was wrong.
Put it on a 15 amp cb or run a 20 amp circuit fo the outlet.
 