I have read other posts, but they don't seem to directly answer my question. If I missed the correct post, I apologize in advance.

I am building a new house, and am paying to have it pre-wired for a hot tub.

The builder's electrician is considering using 6AWG Romex wire for the interior wiring to an outdoor disconnect. The actual hot tub, and therefore the wiring from the disconnect to the hot tub, are not in place. They will be purchased next year. Most of the models that I'm considering are 240v/50a models. They all say that they recommend a 4 WIRE installation.

My understanding is that the Romex wire is 6/3 with an uninsulated ground. I have seen several threads that say this is not an acceptable wire, but the reason seems to be based upon the wire being used outside. This wire will all be used inside. Am I correct in assuming that this wire is unacceptable because it does not have an insulated ground, and that has an effect on the circuit breaker?

The other option, it seems, is to use THHN wire, but that has to be run in conduits (which I prefer not to have). A conduit will require many 90 degree turns, and the electrician says they'll have to use some kind of jumper box in the middle to split up the cable pulls. Does this seem correct?

So we have Romex 6/3+uninsulated ground, or THHN 4 insulated wires in a conduit, or is there another option? Is there anyone who makes a cable of 6/4 wire that would work in the interior of the house?

I am clear on all the Article 680 requirements, and this question is specifically related to the wiring inside the house.

Thanks!

Search Term: HotTub
 

·
Licensed Electrical Cont.
Joined
·
7,829 Posts
6/3NM is perfectly acceptable and typical for the INSIDE portion of the wiring to the disconnect.
 

·
Super Moderator
Joined
·
17,344 Posts
Petey is correct, but some tubs will call for a #6 ground also. The 6-3 NM does not have the #6 ground.
 

·
Registered
Joined
·
6 Posts
Discussion Starter · #4 ·
Thanks, gentlemen, for the responses.

Maybe I misunderstand, but those sound like differing opinions on each side of the question I'm asking.

Speedy Petey is saying 6/3NM is fine and customary inside the house, and Jim Port saying it's not fine, you need insultated ground.

Yes, let's assume that the tub calls for an insulated ground 4WIRE install.

So that's the heart of my quandry.

Does it make a difference if it's from the breaker to the disconnect, or the disconnect to the tub? I mean, could the electrician use 6/3NM from the breaker to the disconect, and then use THHN (in the future) from the disconnect to the hot tub? Or does it need to be THHN with insulated ground all the way through?

Thanks, and Happy St. Patrick's Day to you!
Aidan
 

·
Electrical Contractor
Joined
·
1,994 Posts
Thanks, gentlemen, for the responses.

Maybe I misunderstand, but those sound like differing opinions on each side of the question I'm asking.

Speedy Petey is saying 6/3NM is fine and customary inside the house, and Jim Port saying it's not fine, you need insultated ground.

Yes, let's assume that the tub calls for an insulated ground 4WIRE install.

So that's the heart of my quandry.

Does it make a difference if it's from the breaker to the disconnect, or the disconnect to the tub? I mean, could the electrician use 6/3NM from the breaker to the disconect, and then use THHN (in the future) from the disconnect to the hot tub? Or does it need to be THHN with insulated ground all the way through?

Thanks, and Happy St. Patrick's Day to you!
Aidan
How about running some conduit and pull boxes so the wire can be pulled later when you know for sure what you need.
 

·
Super Moderator
Joined
·
17,344 Posts
The unisulated ground on the inside portion is fine. I have installed hot tubs that called for a #6 ground also. This is not available in 6-3NM so individual conductors would be needed.
 

·
Registered
Joined
·
6 Posts
Discussion Starter · #8 ·
The unisulated ground on the inside portion is fine.
Great. So the builder can use 6-3NM on the inside wiring, and then THHN (later, on the outside portion to the hot tub) with a #6 ground also.

I have installed hot tubs that called for a #6 ground also.
Yes, again, I am assuming that the hot tub calls for a #6 insulated ground. That is typical on the type of tub that I want, and I assume that's what I need.

This is not available in 6-3NM so individual conductors would be needed.
Wait, are you saying that individual conductors are needed, even on the inside?
 

·
Electrical Contractor
Joined
·
1,994 Posts
That's a fine idea, and may end up being what we do. But I'd rather not have the conduit, if I can help it.
If you are required to run individual wires because the need of a #6 ground then you will need conduit anyways.
 
  • Like
Reactions: AidanD55

·
Registered
Joined
·
6 Posts
Discussion Starter · #11 ·
Thank you, Jim Port and rrolleston (also Speedy Peety).

I understand fully now, and I agree with everything you wrote.

I can now be confident in what I am asking for with the builder's electrician.

Thanks,
Aidan
 