Receptacles have no right or left. They have silver screws for neutral, brass screws for hot black and green screw for bare or ground.
Yeah should get pro help in person at this point.I need some help tracking down whats up with the wiring in my living room.
The house was built in 1995.
...inspector told us that half of the outlets in the living room were not grounded
after being in the house a couple of months we bought a tester
...and all the plugs tested normal ... until last night.
six of the outlets tested had a hot to neutral reversed.
the breaker kept tripping so i replaced the 20A breaker,
i checked all the connections... ground wires connected,
white on left, black on right.
I used a voltage meter on the outlets...
the ones showing reversed are testing reversed on the voltage meter (white is hot 120) (black is at 0).
If i plug in the tv the breaker trips again.
If i plug in the tv the breaker trips again.
If you install them right side up, hot is on the right. (OH BOY HERE WE GO AGAIN! :laughingReceptacles have no right or left. They have silver screws for neutral, brass screws for hot black and green screw for bare or ground.
You have a cross somewhere. It might be damaged wire too....with a voltage meter and the black to ground is reading 0 and the white to ground is reading 120 in the six affected recepticles.