Hi Guys/Girls
I have a Rheem Criterion II Model RCBA-3765GG17 from 1995.
I'm new to HVAC and have watched many YouTube videos in the past days and have been able to eliminate many points of failure
I have been working on it for 4 days now and believe I need to replace the control board. I have also been working with a buddy of mine over the phone that is a HVAC Tech, but has left for a hunting trip. He will not return for a couple of more days and cold weather is supposed to be moving in.
During the call for heat, the two green LEDs illuminate and the IDM runs and the blower starts about 10 secs later.
The issue seems to be with the control of Honeywell VR8205H 8016 gas valve and the hot surface igniter. They work, just are not always activated, which I assume is the fault of the control board.
Limits are closed and are getting 26VAC and pressure switch is working correctly. (tested 0 volts across terminals when motor is on) The hot surface ignitor ohms out at 175 which is within its limit.
The igniter does not always heat up (actually very rarely) nor does the gas valve open, although the fan will run almost continuous (30 mins or more)
In the event the igniter does heat up, the gas valve will follow suit and open (This is a strange behavior and why I think the control board needs replaced) Let me explain.
The gas valve should open for about 4 secs whether the hot surface igniter heats up or not but it does not, and when it does open, it is only after the igniter has heated up. It's just strange that they both work and don't work at the same time leading me to believe it is the control board failing to control them correctly.
When these two are working correctly and the burner fires up, it will run until call for heat ends. The gas turns off, but the IDM and blower will run continuously once again as before and thus the igniter and gas valve will fail to start when call for heat is cycled again.
Should note that a power cycle does not resolve this either. To be honest I'm not sure what causes the gas valve and the igniter to start working but it's awesome when it does, but provides me no clues to why it decides to start working properly.
Any advice?
Thanks in advance
Mike
I have a Rheem Criterion II Model RCBA-3765GG17 from 1995.
I'm new to HVAC and have watched many YouTube videos in the past days and have been able to eliminate many points of failure
I have been working on it for 4 days now and believe I need to replace the control board. I have also been working with a buddy of mine over the phone that is a HVAC Tech, but has left for a hunting trip. He will not return for a couple of more days and cold weather is supposed to be moving in.
During the call for heat, the two green LEDs illuminate and the IDM runs and the blower starts about 10 secs later.
The issue seems to be with the control of Honeywell VR8205H 8016 gas valve and the hot surface igniter. They work, just are not always activated, which I assume is the fault of the control board.
Limits are closed and are getting 26VAC and pressure switch is working correctly. (tested 0 volts across terminals when motor is on) The hot surface ignitor ohms out at 175 which is within its limit.
The igniter does not always heat up (actually very rarely) nor does the gas valve open, although the fan will run almost continuous (30 mins or more)
In the event the igniter does heat up, the gas valve will follow suit and open (This is a strange behavior and why I think the control board needs replaced) Let me explain.
The gas valve should open for about 4 secs whether the hot surface igniter heats up or not but it does not, and when it does open, it is only after the igniter has heated up. It's just strange that they both work and don't work at the same time leading me to believe it is the control board failing to control them correctly.
When these two are working correctly and the burner fires up, it will run until call for heat ends. The gas turns off, but the IDM and blower will run continuously once again as before and thus the igniter and gas valve will fail to start when call for heat is cycled again.
Should note that a power cycle does not resolve this either. To be honest I'm not sure what causes the gas valve and the igniter to start working but it's awesome when it does, but provides me no clues to why it decides to start working properly.
Any advice?
Thanks in advance
Mike