My 2nd floor unit was not blowing cold air, it was just blowing lukewarm air. The unit is about 5 years old, and we moved in last summer.

This summer season I decided to get a an annual maintenance done on the unit. The contractor said the Freon was almost empty so he got to filling it up. He cleaned the outside fan as well.

While the Freon was being pumped in gradually I noticed cold air blowing from the vents. When he was done, the unit was cooling. But then I noticed this hissing noise coming from the wall. I put my ear to the wall and it sounds like hissing noise almost like gas escaping. Turned the unit off, the noise went away. Turned the unit back on, and first it sounds like water bubbling/gargling then to develops into a hissing noise.

The annoyance that I have is that the noise is so loud, I can hear it through the wall. The contractor checked the attic and double checked the fan outside, nothing out of place.

He said that the hissing noise is normal, and that it's probably being amplified because the little cooper line is touching the wall somewhere.

Is this normal? The unit is cooling, but that hissing noise is just annoying. Do I need to call someone else over?
 

· Registered
Joined
·
2,881 Posts
I would say it's normal if it's touching the wall. If you can find a way to move it away from the wall it should eliminate the problem. Sounds like you have bigger problems though if the unit was almost empty and the leak was not repaired.
 

· Registered
Joined
·
15,740 Posts
Gurgling is normal at first, but is a sign of low refrigerant if it continues non-stop. The hissing can be a leak or just a vibration being transmitted, hard to say over the internet.

That leak really should be repaired though.

Cheers!
 

· Registered
Joined
·
24 Posts
Discussion Starter · #4 ·
Thank you for the replies. Could the hissing sound be the sound of gas escaping the little copper pipe?

It's loud enough that I hear it upon entering the room about 20 feet away.

If there was low freon to begin with, would the same hissing noises come?
 

· Registered
Joined
·
2,881 Posts
The noise you are hearing is the refrigerant moving through the pipe. The line could be touching the wall. Could be touching the brick and transferring the noise to the wall. Could be air in the lines causing high head pressure. There is a lot of things that could cause it. I'm assuming low in gas is not causing it because the unit was just charged. If you had that big of a leak in the wall the unit would most likely not be cooling already. It's rare to have a leak in the wall but when it happens it's usually caused by some type of construction, picture hanging lol etc
 

· Registered
Joined
·
8,934 Posts
Hissing can happen even with normal operation, it's not a sign that anything is or isn't wrong.
If the unit was low on refrigerant, and no leak was found or repaired, then you will have the same problem again. Refrigerant is not a consumable material, and doesn't need "fill ups". If the charge was incorrect then either it was charged wrong from the start, someone's letting it out or there's a leak.
 

· Hvac Pro
Joined
·
25,191 Posts
The little line is a liquid line and full of liquid refrigerant. It actually sounds like water running. Probably it is touching the wall. If it had a huge leak large enough to hiss then it would leak out in half an hour or less and you would have no cooling.
 

· A "Handy Husband"
Joined
·
15,065 Posts
A leak in the line set would hiss even if you shut down the system (at least until the refrigerant is gone). Don't ask me how I know but it cost me $296.
 

· Registered
Joined
·
15,740 Posts
I agree, if you could hear it through the wall, 20ft away, it isn't a small leak. The wall would likely be cold until the hissing stopped, and you'd be out of refrigerant already. Yes, it "could" be the leak you're looking for, but highly unlikely. If you're still cooling, then it's a much smaller leak, likely one that you can't hear.

Cheers!
 

· Registered
Joined
·
24 Posts
Discussion Starter · #10 ·
Thank you everyone, the comments make a lot of sense.

I didn't think of the fact that if it was a leak then it would be continuous, but the hissing is only present with the ac is on.

16 hours later, the unit is still cooling. I went up to the attic and the noise is there too but much less pronounced. Behind my bedroom wall thought it is the loudest (and this spot happens to be right behind my pillow, sigh)

Since this noise wasn't there before the freon was added, does the loudness of hissing have a positive correlation with the amount of freon injected to the system? Meaning the more that is added the louder the hiss would be, and vice versa.

I'm just thinking if the contractor added more to the system than he was supposed to.
 

· Registered
Joined
·
17,831 Posts
Water flowing sound is healthy and yes higher pressure or higher volume will make the noise more noticeable.

if you hear variations in the sound like gurgling, air bubbles etc there's an issue, granted lots of systems ma have that and cool fine.
 