You have witnessed the dilemma zone (I did not say twilight zone).
Depending on the weather and the time of year, the level of water in the sump pump might come up to a different level and stop. This is because the water table changes.
0. If the pit is completely empty of course the pump does not need to run.
1. If the level stops below the fat drain pipes dumping in then it can probably stay that way indefinitely with the pump not coming on.
3. If the level wants to exceed the floor surface, of course the pump needs to have come on sooner to prevent obvious flooding of the basement.
2. This is the dilemma. If the level covers the fat drain pipes more than about 2/3 then the pump should come on and cycle as needed, even if the water would have stopped one inch above complete submerging of the drain pipes or stops one inch below the surface. Otherwise the behavior of the drain pipe system becomes erratic and you might get random flooding of the opposite side of the basement even with the pit not overflowing.
In all cases the best results are had if, once the pump starts, it keeps going until the pit is almost emptied. Unfortunately some pumps won't let you adjust the float to do this.
If you adjust the float, allow a week of running before concluding that what you did fixed or did not fixthe problem you had.
Adding some bleach or vinegar is a good idea provided that the pump manufacturer does not say it is bad for the plastic parts inside the pump. Do not switch from bleach to vinegar or vice versa without letting the pump run several cycles in between.
Depending on the weather and the time of year, the level of water in the sump pump might come up to a different level and stop. This is because the water table changes.
0. If the pit is completely empty of course the pump does not need to run.
1. If the level stops below the fat drain pipes dumping in then it can probably stay that way indefinitely with the pump not coming on.
3. If the level wants to exceed the floor surface, of course the pump needs to have come on sooner to prevent obvious flooding of the basement.
2. This is the dilemma. If the level covers the fat drain pipes more than about 2/3 then the pump should come on and cycle as needed, even if the water would have stopped one inch above complete submerging of the drain pipes or stops one inch below the surface. Otherwise the behavior of the drain pipe system becomes erratic and you might get random flooding of the opposite side of the basement even with the pit not overflowing.
In all cases the best results are had if, once the pump starts, it keeps going until the pit is almost emptied. Unfortunately some pumps won't let you adjust the float to do this.
If you adjust the float, allow a week of running before concluding that what you did fixed or did not fixthe problem you had.
Adding some bleach or vinegar is a good idea provided that the pump manufacturer does not say it is bad for the plastic parts inside the pump. Do not switch from bleach to vinegar or vice versa without letting the pump run several cycles in between.