Help with proper set-up with Goodman GMV90905DXA and VisionPRO Th8000 series Tstat...

1049 Views 4 Replies 2 Participants Last post by  WGFA
Hi all, I am looking for some guidence on the set-up of these two together. I think I have it but not totally sure. Just want to check on the installation set-up on the VisionPro settings are correct with my Goodman. How would u guys have it set-up? TIA

Here are my set-up settings on my VisionPro:

0170 - 8
0180 - 0
0220 - 2
0230 - 2
0240 - 5
0250 - 5
0300 - 1
0310 - 2
1 - 5 of 5 Posts
Do you actually have a 2 stage A/C?

240-3
250-2
Do you actually have a 2 stage A/C?

240-3
250-2
Good question. Not sure. I assumed that it was 2 stage cool. I am not at home to check the S/N to know if it is 2 stage cool. Other than cool I know its 2 stage Heat. Are my settings maximized for best efficiency?

I looked again at your #'s for "240" & "250" I never noticed 5 was for 90% - and 3 was for 90% +. I have a natural gas so I assume I would use 3 for 240, correct?
TIA
Yes, 240-3
250-2
1 - 5 of 5 Posts