Which code are working under?
Here's some UPC rules-
Clean outs at the base of stacks
Clean outs after 135 degrees(90 & 45) on horizontal runs
Horizontal runs under 5ft- clean outs not needed except sinks & urinals
**Except the bldg drain and its horizontal branches- a cleanout is not required above the floor level of the lowest floor of the building
An approved cleanout is needed where the building drain exits the building
A cleanout may be extended in height by using approved drainage fittings- in your example, bring 3" up through the floor for the cleanout. But you probably don't need that clean out anyways. If you do- you can use the toilet vent if piped properly