Hi, I got a 3rd gen nest for Christmas and I am having a heck of a time making it work. Without the C wire, Nest reports an error with the R wire having no power. When the C wire was connected, it would cause my furnace to constantly turn on and off. From my research, the furnace coming on and off is a power sharing issue that should have been resolved with a C wire. But in my cause, the C wire was causing the issue..
After a few tries I went back to my old thermostat, a Honeywell, that did not require a C wire because it runs on battery. However, since I already connected the C wire I decided to hook it up just in-case the battery runs out and it caused my transformer to blow up.
1. So my question is, why did the transformer malfunction when the C wire was connected? Looking at the furnace diagram, it only shows G-Y-W-R connecting to the thermostat but leaves the C wire terminal empty. Is it possible that it wasn't design for powering a thermostat? The wires are not shorted *tested using continuity with my DDM.
2. I want to run a secondary transformer to power the Nest independently. Can anyone tell me how to do this? I did my best to look on google and youtube but I never found a conclusive answer..
3. To prevent any damages in the future, I decided to rig up a fuse for my replacement transformer.
Should the fuse be placed on the primary side or secondary?I currently have it on the secondary side but i wanted to make sure
How many amps should my fuse be? I currently have a 5 Amp but i believe it should be either 2-3.
My Current setup:
R ------ Thermostat
W ------- Thermostat
Y ------- Thermostat And to the condenser Contactor
G ------- Thermostat
C -------- To the Condenser Contactor and *just recently to Thermostat
Honeywell HQ1009836HW Control Board
120V 24VAC 40VA Transformer
After a few tries I went back to my old thermostat, a Honeywell, that did not require a C wire because it runs on battery. However, since I already connected the C wire I decided to hook it up just in-case the battery runs out and it caused my transformer to blow up.
1. So my question is, why did the transformer malfunction when the C wire was connected? Looking at the furnace diagram, it only shows G-Y-W-R connecting to the thermostat but leaves the C wire terminal empty. Is it possible that it wasn't design for powering a thermostat? The wires are not shorted *tested using continuity with my DDM.
2. I want to run a secondary transformer to power the Nest independently. Can anyone tell me how to do this? I did my best to look on google and youtube but I never found a conclusive answer..
3. To prevent any damages in the future, I decided to rig up a fuse for my replacement transformer.
Should the fuse be placed on the primary side or secondary?I currently have it on the secondary side but i wanted to make sure
How many amps should my fuse be? I currently have a 5 Amp but i believe it should be either 2-3.
My Current setup:
R ------ Thermostat
W ------- Thermostat
Y ------- Thermostat And to the condenser Contactor
G ------- Thermostat
C -------- To the Condenser Contactor and *just recently to Thermostat
Honeywell HQ1009836HW Control Board
120V 24VAC 40VA Transformer