hi. i have a BIG PROBLEM and i need help please.
i have a 30gtn100 carrier that iv been working on for over two days and no hope.

PROBLEMS
AN 8 FLOORS BUILDING WITH TWO OF THE 30gtn100 carrier ON THE ROOF. ALL EIGHT FLOORS ARE ALASKA COLD, THE UNITS ARE NOT CUTTING OFF WHEN IT REACHS A VERY COLD TEMP, AND NO CLLUE WHY, CAN ANY ONE HELP ME PLEASE

AND IS THERE ANY TROUBLE SHOOTING WEBSITE FOR THESE UNITS?

PLEASE PLEASE PLEASE ASAP
 

·
Administrator
Joined
·
41,870 Posts
Where are the thermostats? Or do they use duct stats? What have you checked so far?
 

·
Registered
Joined
·
2 Posts
Discussion Starter · #3 ·
Each room in each floor has a thermostat and I have played with each one of them but no hope
The thermostat works on compressed air, the main line that comes out of the air compressor was broke
And leaking air, after repairing it the pressure is 60 PSI so it’s normal.
I’m almost sure it’s a small problem somewhere but no clue. The air flow does not stop into the building
Plus it is freezing cold 24 hours. I’m not sure if it needs to rest or?
 

·
Administrator
Joined
·
41,870 Posts
Somewhere you will have your pneumatic control panel. Check to see if one or more of the transducers are bad. One of the pneumatic stats may be bad and keeping the unit on.

Those stats are most likely reverse acting, so you may still have an air problem. The control panel should have the pressures you stats work at, make sure they are getting that pressure, and that it is coming back to the transducers/actuators.
 

·
Registered
Joined
·
3,493 Posts
Do you have reheat coils in the system? If you do make sure the heat is on to balance the temp with the humidity. Check your rooftop controls mixed air stats and all dampers, end switches etc.
 