Hi all, I am really hoping someone can help me here as I am sort of running out of options.
I have a 10 year old 90+ Heil furnace in my basement that has been leaking condensation for a few weeks now. I'll try to give as much information as possible so apologies in advance for the long post.
The furnace itself is of the N9Mp1 variety and it is installed "upflow" very similar to Figure 11 in this PDF but with the condensate trap installed outside the unit on the left hand side.
http://icpindexing.toddsit.com/documents/086477/44001102402.pdf
This problem started about 3 weeks ago when I noticed water on the floor of the basement. Removing the top cover revealed the black transition box was leaking. I ordered a replacement which came with a soft foam gasket in between it and the exhaust blower. If you look at the exploded diagram in the above PDF these are items "P" and "Q" in the picture.
After I replaced those I put the furnace back together and that has solved the leak there. HOWEVER two new leak have appeared which I am currently dealing with.
The first is from the black 5/8" OD 1/2" ID rubber tube running from the Exhaust pipe connector to the condensate trap. This tube is seized and badly cracked so water is leaking out of there, not a lot, maybe 5-10 milliliters every 2 hours or so, but definitely enough that it's a problem.
To fix this I have ordered a new hose which I'm waiting on to arrive.
The big problem which I've no solution for is that water seems to be seeping out from underneath the metal enclosing the secondary heat exchanger. Again, not a lot but enough that it's a problem and I've no idea where this is coming from.
Things I've done:
- I can't touch the 5/8" hose as it'll crack if I breath on it but I've taken off the other hoses, the 1/2" "elbow" and the smaller 3/16" tube and made sure these are clear.
- I've taken upper caps off the condensate and tried to clean this out with a very small (1cm diameter) bristle type pipe cleaner brush. Nothing much came out.
- I've poured a few oz of Draino into the condensate trap and let it sit for about 20mins. Then I flushed it with warm water from the kettle (not boiling). I was able to pour a constant stream of water from the kettle into the condensate trap using a small funnel and it drained away no problem.
This morning I took the cover off whilst the furnace was running and noticed water under the metal partition behind the transition box. Whilst the unit was running I noticed this water seems to "wisp" in and out almost like something was sucking on it from behind the partition but then losing suction and the water flows back towards me. I think this suction is caused by the Exhaust blower (item #11 from page 60 in the above PDF).
Couple of questions:
- Why does the manual say to "prime" the condensate trap with 8oz of water? It looks like this is just a plastic box but the fact that they suggest priming it indicates there's some kind of seal inside that needs to be wetted in order to maybe created a pressurised loop of some kind.
- The system still needs a new hose. Is it possible it's relying on pressure to pump the water to the trap and as a result of the cracked hose the water is not making it to the condensate trap?
- Is this water actually produced in the secondary heat exchanger area or is it produced in the transition box and somehow finding its way back from the transition box into that area?
- One theory I had was it's produced in the transition box and not draining out of it sufficiently fast. Then backing up into the row of circular holes in the secondary heat exchanger which the transition box covers and finally leaking down from the cover.
- Should the bottom of the metal partition between the secondary heat exchanger and the transition box be air-tight with the floor of the top part of the furnace? It currently is not and this is where I saw the water wisping in and out.
- The Exhaust blower runs AFTER the gas burners turn off. Then after a few seconds the gas blowers will turn back on and burn more. I think this is not supposed to happen but am assuming for now it's related to this leak I have.
Again, apologies for the long message. I have attached some photos to clarify some of this.
Meanwhile any and all help is GREATLY appreciated. I have been unable to locate anyone who'll touch this thing with a long stick and have been losing sleep on it for a long time now.
I would really love to just open the door some day and find the unit to be bone dry. Help me get there DIYers!!!
I have a 10 year old 90+ Heil furnace in my basement that has been leaking condensation for a few weeks now. I'll try to give as much information as possible so apologies in advance for the long post.
The furnace itself is of the N9Mp1 variety and it is installed "upflow" very similar to Figure 11 in this PDF but with the condensate trap installed outside the unit on the left hand side.
http://icpindexing.toddsit.com/documents/086477/44001102402.pdf
This problem started about 3 weeks ago when I noticed water on the floor of the basement. Removing the top cover revealed the black transition box was leaking. I ordered a replacement which came with a soft foam gasket in between it and the exhaust blower. If you look at the exploded diagram in the above PDF these are items "P" and "Q" in the picture.
After I replaced those I put the furnace back together and that has solved the leak there. HOWEVER two new leak have appeared which I am currently dealing with.
The first is from the black 5/8" OD 1/2" ID rubber tube running from the Exhaust pipe connector to the condensate trap. This tube is seized and badly cracked so water is leaking out of there, not a lot, maybe 5-10 milliliters every 2 hours or so, but definitely enough that it's a problem.
To fix this I have ordered a new hose which I'm waiting on to arrive.
The big problem which I've no solution for is that water seems to be seeping out from underneath the metal enclosing the secondary heat exchanger. Again, not a lot but enough that it's a problem and I've no idea where this is coming from.
Things I've done:
- I can't touch the 5/8" hose as it'll crack if I breath on it but I've taken off the other hoses, the 1/2" "elbow" and the smaller 3/16" tube and made sure these are clear.
- I've taken upper caps off the condensate and tried to clean this out with a very small (1cm diameter) bristle type pipe cleaner brush. Nothing much came out.
- I've poured a few oz of Draino into the condensate trap and let it sit for about 20mins. Then I flushed it with warm water from the kettle (not boiling). I was able to pour a constant stream of water from the kettle into the condensate trap using a small funnel and it drained away no problem.
This morning I took the cover off whilst the furnace was running and noticed water under the metal partition behind the transition box. Whilst the unit was running I noticed this water seems to "wisp" in and out almost like something was sucking on it from behind the partition but then losing suction and the water flows back towards me. I think this suction is caused by the Exhaust blower (item #11 from page 60 in the above PDF).
Couple of questions:
- Why does the manual say to "prime" the condensate trap with 8oz of water? It looks like this is just a plastic box but the fact that they suggest priming it indicates there's some kind of seal inside that needs to be wetted in order to maybe created a pressurised loop of some kind.
- The system still needs a new hose. Is it possible it's relying on pressure to pump the water to the trap and as a result of the cracked hose the water is not making it to the condensate trap?
- Is this water actually produced in the secondary heat exchanger area or is it produced in the transition box and somehow finding its way back from the transition box into that area?
- One theory I had was it's produced in the transition box and not draining out of it sufficiently fast. Then backing up into the row of circular holes in the secondary heat exchanger which the transition box covers and finally leaking down from the cover.
- Should the bottom of the metal partition between the secondary heat exchanger and the transition box be air-tight with the floor of the top part of the furnace? It currently is not and this is where I saw the water wisping in and out.
- The Exhaust blower runs AFTER the gas burners turn off. Then after a few seconds the gas blowers will turn back on and burn more. I think this is not supposed to happen but am assuming for now it's related to this leak I have.
Again, apologies for the long message. I have attached some photos to clarify some of this.
Meanwhile any and all help is GREATLY appreciated. I have been unable to locate anyone who'll touch this thing with a long stick and have been losing sleep on it for a long time now.
I would really love to just open the door some day and find the unit to be bone dry. Help me get there DIYers!!!