1885 house with breaker box installed in the 19 70 s or 80s . It is currently level with the kitchen floor. Is this legal...when did the code change the height of abreaker box...is it safe the way it is or do we have to raise the height.
Is it legal as it pre dates code ?
 

· Banned
Joined
·
17,162 Posts
1885 house with breaker box installed in the 19 70 s or 80s . It is currently level with the kitchen floor. Is this legal...when did the code change the height of abreaker box...is it safe the way it is or do we have to raise the height.
Is it legal as it pre dates code ?
Actually it will pass. You would be surprised what you find in old homes that would still pass today's codes.

Really it needs to be moved up to at least 36"-48" from the floor. No one likes laying on the floor to work on a breaker/fuse panel.
 

· Registered
Joined
·
775 Posts
As Jim stated, there is no minimum height requirement only maximum. The only grandfathered code I know of pertaining to this is overhead clearance exclusions for existing residential panels. I've never seen anything about 36-48" off the floor although it would be nice.
 

· Registered
Joined
·
13 Posts
Discussion Starter · #6 ·
I have now had 3-4 local electricians look and tell me that it isent code because it's at a dangerous height...it's at floor level.
What nec code number should I quote when being asked for $1500 to raise the breaker box 4 ft. The last electrician even threatened me with calling in the fire Marshall if i dident pay him to raise it.
 

· Registered
Joined
·
13 Posts
Discussion Starter · #8 ·
I am confused. Why are you calling in local electricians? And as a point of order, the opinion of a local electrician means nothing, the only opinion that counts is your local electrical inspector.
Well we need a circuit checked as its tripping out a breaker but when the electrician saw the box he said it's not code because it's at floor level....
 

· Super Moderator
Joined
·
24,969 Posts
I don't know about the NEC but in Ontario code states

Panelboards in dwelling units shall be mounted as high as possible but with no circuit breaker position higher than 1.7 m (5' 6") above the finished floor level.

Rule 26-402.

Ontario Electrical Safety Code 25th Edition/2012.
Note the "as high as possible" part of code.
 

· Registered
Joined
·
249 Posts
NEC 240.24 Location in or on Premises
(A) Accessibility. Overcurrent devices shall be readily accessible
and shall be installed so that the center of the grip of the
operating handle of the switch or circuit breaker, when in its
highest position, is not more than 2.0 m (6 ft 7 in.) above the
floor or working platform, unless one of the following applies:
(1) For busways, as provided in 368.17(C).
(2) For supplementary overcurrent protection, as described in
240.10.
(3) For overcurrent devices, as described in 225.40 and 230.92.
(4) For overcurrent devices adjacent to utilization equipment
that they supply, access shall be permitted to be by portable
means.
 

· Banned
Joined
·
17,162 Posts
I have now had 3-4 local electricians look and tell me that it isent code because it's at a dangerous height...it's at floor level.
What nec code number should I quote when being asked for $1500 to raise the breaker box 4 ft. The last electrician even threatened me with calling in the fire Marshall if i dident pay him to raise it.
There can be a local code. Nothing other then clearance on sides and top. You will usually find them around 4' off of floors, so that they are not hidden by couches, chairs or tables.

"NEC Guidelines On Breaker Panels

The National Electrical Codes or NEC are produced through the National Fire Protection Association. Although the codes are not law, they are used as a reference for state and local authorities on which to base building codes relating to electrical wiring. The NEC specifically addresses breaker panels in Article 110 of the regulatory guidelines, addressed as “Requirements of Electrical Installations.”

For breaker panels, an area referred to as the “working space” is the area around the breaker panel that must be free of any other installations. According to the NEC, the working space around the breaker panel must be at least 6′ 6” high and 3 feet square away from the wall, with 30” width. This allows the door to be opened to the panel, with nothing blocking the area.
The working handle of the highest center grip should not be more than 6′ 7” from the floor.
Breaker panels should not be located in small, enclosed rooms such as a closet, bathroom, pantry or small storage room.
Breaker panels must be easily accessible. No furniture or other obstructions should be placed in the working space, making it easy to approach the front of the panel.
Illumination of the area is essential. Although having a light in the room of the breaker panel may be considered sufficient by code, it may be worth dedicating a circuit to a light above the panel. This gives direct light to make it easy to see switches in dim conditions.
Best Locations For Breaker Panels

When deciding where to position a breaker panel, a few factors should be considered. The panel or box will need to be easily accessible; however, most people also want the box out of view, especially in a home or business. The trick is to find an area that is large enough to meet the working space standards set by the NEC, and that is out of sight, while still easy to access. Some common areas that may meet these stipulations include:

Under stairways. If there is sufficient space, breaker panels can be placed under the stairs where there is easy access.
Garages. For homes with attached garages, this is the perfect place for installing a breaker panel. An area near the door that connects to the garage would be a good choice.
Basements. Many homes and buildings have the breaker panel in the basement. Just ensure that there is enough emergency lighting in case of a power outage to find the box in the dark.
Of course, breaker panels can be put in main areas of the home or business, although most people prefer to have them out of sight. If they are in main areas, it is possible to paint the door or box of the panel to match the décor. However, they should not be covered with pictures or other ornaments that could make them difficult to find or access. The main considerations should be that the working space is adhered to, along with easy accessibility and illumination."

http://m.ecmweb.com/code-basics/determining-working-clearances

http://m.ecmweb.com/code-basics/switchboards-and-panels
 

· Lic Electrical Inspector
Joined
·
1,844 Posts
Matt bryan said:
Well we need a circuit checked as its tripping out a breaker but when the electrician saw the box he said it's not code because it's at floor level....
If your local electricians are telling you it's against code they should be able to tell the specific code section. Other than a possible local amendment or manufacturer there is nothing on the NEC that sets a minimum height. Sounds like you red to find someone who actually knows what they are ta