Height from ground for Fresh Air Intake

1834 Views 5 Replies 2 Participants Last post by  beenthere
I need to install a fresh air intake to the basement, and wondering what sort of clearance I should have from the ground. I've got a bit over 2 feet between ground level and the subfloor. I'm in Minnesota, so I ask because of the potential for snow to block the intake.
1 - 3 of 6 Posts
12" above normal snow fall accumulation level.
Goose neck it.
By code, 68 sq inches of cross section. 9" round. Many contactors just run a single 6".
1 - 3 of 6 Posts