Discussion Starter · #1 ·
As one would know it, this cold weather cased a pipe to rupture in our garage. I found the shutoff valve for the garage base board. Looking at the water pressure, I saw their was none. So online, found how to use the water safety valve to add more water to the system. However, the manual did not say what the max pressure was. We have a New Yorker FR-95 / 122 W. Would anyone know what those specks would be, or where I could find them?

LBourdon
 

· Registered
Joined
·
1,565 Posts
Pressure is controlled by the number of stories . A two story house will have a cold pressure of maybe 15 psi. The expansion tank will keep this relatively constant but it will go a couple of psi when heated. A hydronic system is relatively low pressure
 