I am not an air conditioning expert! I learn through trial and error. Here is the issue, my Draft Inducer Motor and the main fan that blows air into our vents does not turn off! The only way I can turn it off is by flipping the breaker off. As soon as I turn the breaker back on, the Draft Inducer Motor and main fan that blows air into our vents immediately starts blowing! With regards to the thermostat...I have turned it off, but this does not make the Draft Inducer Motor or main fan stop! I remove the batteries and it does NOT make the Draft Inducer Motor or main fan stop! Only by flipping the breaker does everything shut off. Now, the heater lights up and works perfectly and blows hot air into vents AND the air conditioner works perfectly and blows cold air into vents. If I lower the heat to below the current temperature, the heat does turn off, but again the Draft Inducer Motor and the main fan continue to blow air!
In the last 6 months, I have changed the following: Dual Run Capacitor, Run Capacitor, Pressure Switch, Flame Rollout Limit Switch, and air filter every 3 months! Lastly, I changed the Control Board a year ago. The fuse is not broken!
This is on York unit that is 10+ years old and resides on the top roof of our condominium.
· In Loving Memory
Depending on which model you have. There may be a fan limit combo inside the heat exchanger compartment. That the fan switch may be closed causing both the inducer and fan to stay on. Access to it is from the opposite side of the burner compartment.
Your model may or may not have it.
If it doesn't, see if the induce and fan run if you disconnect the wires from the RTU's W and G terminals.
Reactions: supers05
Older york rooftops use a 3 way high limit. When craps gets in the contacts it can conduct to both pins. Powering the fan and inducer, but doesn't lock out heat. (In even older models, it'll keep the burner on until people start melting and call for help... Yikes... )
Cheers!