Where is the duct work? Strung up in the air? In a hot attic?
Our 30 ft. of 14" flex return in the attic was gaining about 4-6°F until i added another 2" layer of similar plastic wrapped insulation. The heat gain was reduced to around 0.6°F.
Did you take off the foil vapor barrier first? My thought is that it shouldn't be sandwhiched between two layers of insulation.
The original ( plastic ) vapor barrier is still there and has been for about 35 years.Our 30 ft. of 14" flex return in the attic was gaining about 4-6°F until i added another 2" layer of similar plastic wrapped insulation. The heat gain was reduced to around 0.6°F.
Did you take off the foil vapor barrier first? My thought is that it shouldn't be sandwhiched between two layers of insulation.
Thank you. So you basically used a new foil insulation blanket to wrap around the existing flex?? Did you use foil tape to tape the seams in the new insulation?The original ( plastic ) vapor barrier is still there and has been for about 35 years.
Plastic wrap over original plastic wrap. It's been so long since i've been in the attic i really don't recall what tape was used, sorry. I've since used aluminum tape of several projects and really like it, although it isn't nearly as convenient as that good old duck tape.Thank you. So you basically used a new foil insulation blanket to wrap around the existing flex?? Did you use foil tape to tape the seams in the new insulation?